    • M-A Hueb
      M-A Hueb last edited by

      Mal ne doofe Frage, warum sind bei manchen die Mod-Bus Adressen für den Akku bei 50000 und bei manchen im 100000 er Bereich? Wonach richtet sich das?

      1 Reply Last reply Reply Quote 0
      • Glasfaser
        Glasfaser @Longbow last edited by Glasfaser

        @longbow sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

        dort wird ja dann abgezogen.

        Nimm nochmal diese Script zusätzlich

        <xml xmlns="https://developers.google.com/blockly/xml">
         <block type="procedures_defcustomnoreturn" id="Yo~vdCDoW+:y6C:Z%jLM" x="363" y="-87">
           <mutation statements="false"></mutation>
           <field name="NAME">etwas tun</field>
           <field name="SCRIPT">Y3JlYXRlU3RhdGUoJ1NvbGFyLldlY2hzZWxyaWNodGVyLlBWTGVpc3R1bmdBa3R1ZWxsX2JlaVNwZWljaGVybGFkdW5nJywgew0KDQoJbmFtZTogJ1BWTGVpc3R1bmdBa3R1ZWxsX2JlaVNwZWljaGVybGFkdW5nJywNCg0KCXVuaXQ6ICdXJywNCg0KCW1pbjogIDAsDQoNCgl0eXBlOiAnbnVtYmVyJywNCg0KCXJvbGU6ICd2YWx1ZS5lbmVyZ3knDQp9KTsNCg==</field>
           <comment pinned="false" h="80" w="160">Beschreibe diese Funktion …</comment>
         </block>
         <block type="on_ext" id="0WNw^]CyfADZ9h[46/yr" x="88" y="113">
           <mutation xmlns="http://www.w3.org/1999/xhtml" items="1"></mutation>
           <field name="CONDITION">any</field>
           <field name="ACK_CONDITION"></field>
           <value name="OID0">
             <shadow type="field_oid" id="aHInbBr3)gU07u~$!]S=">
               <field name="oid">javascript.0.Solar.Wechselrichter.PVLeistungAktuell</field>
             </shadow>
           </value>
           <statement name="STATEMENT">
             <block type="controls_if" id="eEZ^;:%^di=,nx/+1pa:">
               <mutation else="1"></mutation>
               <value name="IF0">
                 <block type="logic_compare" id="YF9_}bG6}dO/o^2wBUu$">
                   <field name="OP">EQ</field>
                   <value name="A">
                     <block type="get_value" id="lZVMH870OLT)=jiM(:J*">
                       <field name="ATTR">val</field>
                       <field name="OID">modbus.3.holdingRegisters.57734_Battery_1_Status</field>
                     </block>
                   </value>
                   <value name="B">
                     <block type="math_number" id="E=,rcU`PAPqzGdD;z#ph">
                       <field name="NUM">3</field>
                     </block>
                   </value>
                 </block>
               </value>
               <statement name="DO0">
                 <block type="update" id="=U8B5_HREC.%ywC@*NUX">
                   <mutation xmlns="http://www.w3.org/1999/xhtml" delay_input="false"></mutation>
                   <field name="OID">javascript.0.Solar.Wechselrichter.PVLeistungAktuell_Dachflaeche</field>
                   <field name="WITH_DELAY">FALSE</field>
                   <value name="VALUE">
                     <block type="math_arithmetic" id="k1ql[z$jjxr4y2epe^yv">
                       <field name="OP">ADD</field>
                       <value name="A">
                         <shadow type="math_number" id="sJp~@vx71!N=60lSV@tn">
                           <field name="NUM">1</field>
                         </shadow>
                         <block type="on_source" id="veT._9tKCvSl?bikEiqC">
                           <field name="ATTR">state.val</field>
                         </block>
                       </value>
                       <value name="B">
                         <shadow type="math_number" id="Npe:FP|KT.MC?$=;iBKQ">
                           <field name="NUM">1</field>
                         </shadow>
                         <block type="get_value" id="t;_RJ9`t0KjSVRPVS#lg">
                           <field name="ATTR">val</field>
                           <field name="OID">javascript.0.Solar.Wechselrichter.Batterie Lade-Leistung</field>
                         </block>
                       </value>
                     </block>
                   </value>
                 </block>
               </statement>
               <statement name="ELSE">
                 <block type="update" id="f%6W0:Whp*sI$jQnfGq[">
                   <mutation xmlns="http://www.w3.org/1999/xhtml" delay_input="false"></mutation>
                   <field name="OID">javascript.0.Solar.Wechselrichter.PVLeistungAktuell_Dachflaeche</field>
                   <field name="WITH_DELAY">FALSE</field>
                   <value name="VALUE">
                     <block type="get_value" id="vcJf8wafqvdEnyO*zP10">
                       <field name="ATTR">val</field>
                       <field name="OID">javascript.0.Solar.Wechselrichter.PVLeistungAktuell_ohneSpeicher</field>
                     </block>
                   </value>
                 </block>
               </statement>
             </block>
           </statement>
         </block>
        </xml>
        

        javascript.0.Solar.Wechselrichter.PVLeistungAktuell_Dachflaeche , mußt du noch selber anlegen
        Die anderen Datenpunkte auf deine ändern

        Longbow 1 Reply Last reply Reply Quote 0
        • Longbow
          Longbow @Glasfaser last edited by

          @glasfaser Danke, habe ich soweit gemacht... bekomme aber diese Fehlermeldung.

          
          javascript.0
          2023-06-13 19:13:03.378	error	at processImmediate (node:internal/timers:468:21)
          
          javascript.0
          2023-06-13 19:13:03.378	error	at Immediate._onImmediate (/opt/iobroker/node_modules/iobroker.javascript/main.js:1527:17)
          
          javascript.0
          2023-06-13 19:13:03.378	error	at /opt/iobroker/node_modules/iobroker.javascript/main.js:2053:17
          
          javascript.0
          2023-06-13 19:13:03.377	error	at prepareScript (/opt/iobroker/node_modules/iobroker.javascript/main.js:1955:37)
          
          javascript.0
          2023-06-13 19:13:03.377	error	at createVM (/opt/iobroker/node_modules/iobroker.javascript/main.js:1702:21)
          
          javascript.0
          2023-06-13 19:13:03.377	error	at new Script (node:vm:100:7)
          
          javascript.0
          2023-06-13 19:13:03.377	error	SyntaxError: Unexpected token '<'
          
          javascript.0
          2023-06-13 19:13:03.377	error	^
          
          javascript.0
          2023-06-13 19:13:03.377	error	<xml xmlns="https://developers.google.com/blockly/xml">
          
          javascript.0
          2023-06-13 19:13:03.377	error	script.js.common.PV-SolarEgde.PVLeistungAktuelle_Dachflaeche compile failed: at script.js.common.PV-SolarEgde.PVLeistungAktuelle_Dachflaeche:1
          
          Glasfaser 1 Reply Last reply Reply Quote 0
          • Glasfaser
            Glasfaser @Longbow last edited by

            @longbow

            Beim einfügen schon diese Meldung ...

            Das Blockly funktioniert , gerade mal neu eingefügt in Js .

            Da ist nicht viel drin ...

            .
            1120bc12-0b88-4eac-a2da-9a18a8fbc4b0-grafik.png

            Longbow 1 Reply Last reply Reply Quote 0
            • Longbow
              Longbow @Glasfaser last edited by

              @glasfaser Guten Morgen, keine Ahnung warum auch immer, hab es gelöscht, erneut und wieder importiert und es klappt nun. Vielen Dank aber jetzt... So langsam verstehe ich auch das was man mit Scripts machen kann. 🙂

              1 Reply Last reply Reply Quote 0
              • A
                Apfel85 last edited by

                Hallo zusammen,

                ich bin neu hier und verfolge mit großem Interesse dem Thema. An dieser Stelle vielen Dank für all die Infos, welche bereits im Thread gesammelt wurden.

                Leider stehe ich vor einem kleinen Batterieproblem..... Ich besitze eine PV-Anlage mit 2 SE Wechselrichtern. Am Hybridwechselrichter ist ein Batteriespeicher angeschlossen. Diesen kann ich mitterweile sehr gut auslesen mit ein paar Ausnahmen. Hat jemand dieses Problem schonmal gehabt bzw. wenn es bei euch nicht existiert, wie sind die Modbuseinstellungen zu sezten?

                1. Die max. Temperatur bleibt immer bei 0°C - hat sich auch noch nie geändert
                2. Die TotalExport Werte schwanken stark - setzen sich auch immer wieder auf 0 zurück. Habe die Adresse mit 2 unterschiedlichen Typen zum Test gepflegt
                3. Selbiges hab ich mit den TotalImport Werten

                Hier ein Auszug aus meinen Ergebnissen
                2023-07-17_14-08-42.jpg

                Hier die Total Import und Export Werte in kWh
                2023-07-17_14-21-10.jpg

                Hier die angelegten Adressen:

                _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	poll	wp	cw	isScale
                97601	1	Batt1_Manufacturer			string	8	1	0				true	false	false	false
                97617	1	Batt1_Model			string	16	1	0				true	false	false	false
                97633	1	Batt1_Firmware			string	16	1	0				true	false	false	false
                97649	1	Batt1_Serial			string	16	1	0				true	false	false	false
                97665	1	Batt1_ID	Device ID		uint16be	1	1	0				true	false	false	false
                97667	1	Batt1_RatedEnergy	Nennenergie	kWh	floatsw	2	1	0	x * Math.pow(10, -3)			true	false	false	false
                97669	1	Batt1_MaxChargeConPower	Max. Ladeleistung Fortlaufend	W	floatsw	2	1	0				true	false	false	false
                97671	1	Batt1_MaxDischargeConPower	 Max. Entladeleistung Fortlaufend	W	floatsw	2	1	0				true	false	false	false
                97673	1	Batt1_MaxChargePower	Max. Ladeleistung	W	floatsw	2	1	0				true	false	false	false
                97675	1	Batt1_MaxDischargePower	Max. Entladeleistung	W	floatsw	2	1	0				true	false	false	false
                97709	1	Batt1_AverageTemp	Durchschnittstemperatur	°C	floatsw	2	1	0				true	false	false	false
                97711	1	Batt1_MaxTemp	Maximale Temperatur	°C	floatsw	2	1	0				true	false	false	false
                97713	1	Batt1_Voltage	Aktuelle Spannung	V	floatsw	2	1	0				true	false	false	false
                97715	1	Batt1_Current	Aktueller Strom Minus = Laden; Plus = Entladen	A	floatsw	2	1	0				true	false	false	false
                97717	1	Batt1_Power	Aktuelle Leistung Minus = Entladen; Plus = Laden	W	floatsw	2	1	0				true	false	false	false
                97719	1	Batt1_TotalExport	gesamt Exportierte Energie - heute?	kWh	uint32sw	2	1	0	x * Math.pow(10, -3)			true	false	false	false
                97719	1	Batt1_TestExport		kWh	uint64le	4	1	0	x * Math.pow(10, -3)			true	false	false	false
                97723	1	Batt1_TotalImport	gesamt Importierte Energie - heute?	kWh	uint32sw	2	1	0	x * Math.pow(10, -3)			true	false	false	false
                97723	1	Batt1_TestImport		kWh	uint64le	4	1	0	x * Math.pow(10, -3)			true	false	false	false
                97727	1	Batt1_MaxEnergy	Maximale Ladung	kWh	floatsw	2	1	0	x * Math.pow(10, -3)			true	false	false	false
                97729	1	Batt1_AvailableEnergy	Nutzbare Ladung	kWh	floatsw	2	1	0	x * Math.pow(10, -3)			true	false	false	false
                97731	1	Batt1_StateOfHealth	Lebenszustand	%	floatsw	2	1	0				true	false	false	false
                97733	1	Batt1_StateOfCharge	Ladezustand	%	floatsw	2	1	0				true	false	false	false
                97735	1	Batt1_Status	Battery operating state: 0 – Off; 1 – Standby; 2 – Init; 3 – Charge; 4 – Discharge; 5 – Fault; 7 - Idle		uint32sw	2	1	0				true	false	false	false
                97737	1	Batt1_StatusIntern	Vendor-defined status codes.		uint32sw	2	1	0				true	false	false	false
                97739	1	Batt1_EventLog	Battery vendor's last fault ID		uint16le	1	1	0				true	false	false	false
                40001	1	C_SunSpec_ID	"Wert = ""SunS"" (0x53756e53). Identifiziert dies eindeutig als eine SunSpec Modbus-Karte"		uint32be	2	1	0				true	false	false	false
                40003	1	C_SunSpec_DID	Wert = 0x0001. Identifiziert dies eindeutig als einen SunSpec “Common Block“		uint16be	1	1	0				true	false	false	false
                40004	1	C_SunSpec_Length	65 = Länge eines Blocks in 16-bit Registern		uint16be	1	1	0				true	false	false	false
                40005	1	C_Manufacturer	"Bei SunSpec eingetragener Wert = ""SolarEdge"""		string	16	1	0				true	false	false	false
                40021	1	C_Model	Spezifischer SolarEdge Wert		string	16	1	0				true	false	false	false
                40045	1	C_Version	Spezifischer SolarEdge Wert		string	8	1	0				true	false	false	false
                40053	1	C_SerialNumber	Eindeutiger SolarEdge Wert		string	16	1	0				true	false	false	false
                40069	1	C_DeviceAddress 	Modbus-ID der entsprechenden Einheit		uint16be	1	1	0				true	false	false	false
                40070	1	C_SunSpec_DID	101 = Einphasig, 102 = Spaltphase, 103 = Dreiphasig		uint16be	1	1	0				true	false	false	false
                40072	1	I_AC_Current	AC-Strom Gesamtstromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40076'])			true	false	false	false
                40073	1	I_AC_CurrentA	AC-Strom Phase A (L1) Stromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40076'])			true	false	false	false
                40074	1	I_AC_CurrentB	AC-Strom Phase B (L2) Stromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40076'])			true	false	false	false
                40075	1	I_AC_CurrentC	AC-Strom Phase C (L3) Stromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40076'])			true	false	false	false
                40076	1	I_AC_Current_SF	AC-Strom Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40084	1	I_AC_Power	AC-Leistung Leistungswert	W	int16be	1	1	0	x * Math.pow(10, sf['40085'])			true	false	false	false
                40085	1	I_AC_Power_SF	AC-Leistung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40088	1	I_AC_VA	Scheinleistung	VA	int16be	1	1	0	x * Math.pow(10, sf['40089'])			true	false	false	false
                40089	1	I_AC_VA_SF	Scheinleistung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40090	1	I_AC_VAR	Blindleistung	VAR	int16be	1	1	0	x * Math.pow(10, sf['40091'])			true	false	false	false
                40091	1	I_AC_VAR_SF	Blindleistung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40092	1	I_AC_PF	Leistungsfaktor %	%	int16be	1	1	0	x * Math.pow(10, sf['40093'])			true	false	false	false
                40093	1	I_AC_PF_SF	Leistungsfaktor Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40094	1	I_AC_Energy_WH	AC Energie Gesamt-Energieproduktion	kWh	uint32be	2	1	0	x * Math.pow(10, sf['40096'] - 3)			true	false	false	false
                40096	1	I_AC_Energy_WH_SF	AC Energie Gesamtenergie Skalierungsfaktor	SF	uint16be	1	1	0				true	false	false	true
                40097	1	I_DC_Current	DC-Strom Stromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40098'])			true	false	false	false
                40098	1	I_DC_Current_SF	DC-Strom Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40099	1	I_DC_Voltage	DC-Spannung Spannungswert	V	uint16be	1	1	0	x * Math.pow(10, sf['40100'])			true	false	false	false
                40100	1	I_DC_Voltage_SF	DC-Spannung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40101	1	I_DC_Power	DC-Leistung Leistungswert	W	int16be	1	1	0	x * Math.pow(10, sf['40102'])			true	false	false	false
                40102	1	I_DC_Power_SF	DC-Leistung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40104	1	I_Temp_Sink	Kühlkörpertemperatur	°C	int16be	1	1	0	x * Math.pow(10, sf['40107'])			true	false	false	false
                40107	1	I_Temp_SF	Kühlkörpertemperatur Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40108	1	I_Status	Betriebszustand (1 = Aus, 2 = Schlafen (Automatisches Herunterfahren) – Nachtmodus, 3 = Aufwachen/Starten, 4 = Wechselrichter ist AN und wandelt Energie, 5 = Begrenzte Produktion, 6 = Herunterfahren, 7 = Fehler, 8 = Wartung/Setup)		uint16be	1	1	0				true	false	false	false
                40109	1	I_Status_Vendor	Anbieter-spezifischer Betriebszustand sowie Fehlercodes: 1 = Aus, 2 = Schlafen (Automatisches Herunterfahren) – Nachtmodus, 3 = Aufwachen/Starten, 4 = Wechselrichter ist AN und wandelt Energie, 5 = Begrenzte Produktion, 6 = Herunterfahren, 7 = Fehler, 8 = Wartung/Setup		uint16be	1	1	0				true	false	false	false
                40124	1	C_Manufacturer	Meter manufacturer		string	16	1	0				true	false	false	false
                40140	1	C_Model	Meter model		string	16	1	0				true	false	false	false
                40156	1	C_Option	Export + Import, Production, consumption		string	8	1	0				true	false	false	false
                40164	1	C_Version	Meter version		string	8	1	0				true	false	false	false
                40191	1	M_AC_Current	AC Current (sum of active phases)	A	int16be	1	1	0	x * Math.pow(10, sf['40195'])			true	false	false	false
                40192	1	M_AC_Current_A	Phase A AC Current	A	int16be	1	1	0	x * Math.pow(10, sf['40195'])			true	false	false	false
                40193	1	M_AC_Current_B	Phase B AC Current	A	int16be	1	1	0	x * Math.pow(10, sf['40195'])			true	false	false	false
                40194	1	M_AC_Current_C	Phase C AC Current	A	int16be	1	1	0	x * Math.pow(10, sf['40195'])			true	false	false	false
                40195	1	M_AC_Current_S F	AC Current Scale Factor	SF	int16be	1	1	0				true	false	false	true
                40207	1	M_AC_Power	Total real power (sum of active phases) Minus = Bezug; Plus = Einspeisung	W	int16be	1	1	0	x * Math.pow(10, sf['40211'])			true	false	false	false
                40211	1	M_AC_Power_SF	AC Real Power Scale Factor	SF	int16be	1	1	0				true	false	false	true
                40222	1	M_AC_PF	Average Power Factor (average of active phases)	%	int16be	1	1	0	x * Math.pow(10, sf['40226'])			true	false	false	false
                40226	1	M_AC_PF_SF	AC Power Factor Scale Factor	SF	int16be	1	1	0				true	false	false	true
                40227	1	M_Exported	Total Exported Real Energy	kWh	uint32be	2	1	0	x * Math.pow(10, sf['40243'] -3)			true	false	false	false
                40235	1	M_Imported	Total Imported Real Energy	kWh	uint32be	2	1	0	x * Math.pow(10, sf['40243'] -3)			true	false	false	false
                40243	1	M_Energy_W_SF	Real Energy Scale Factor	SF	int16be	1	1	0				true	false	false	true
                40005	2	C_Manufacturer	"Bei SunSpec eingetragener Wert = ""SolarEdge"""		string	16	1	0				true	false	false	false
                40021	2	C_Model	Spezifischer SolarEdge Wert		string	16	1	0				true	false	false	false
                40045	2	C_Version	Spezifischer SolarEdge Wert		string	8	1	0				true	false	false	false
                40053	2	C_SerialNumber	Eindeutiger SolarEdge Wert		string	16	1	0				true	false	false	false
                40069	2	C_DeviceAddress 	Modbus-ID der entsprechenden Einheit		uint16be	1	1	0				true	false	false	false
                40070	2	C_SunSpec_DID	101 = Einphasig, 102 = Spaltphase, 103 = Dreiphasig		uint16be	1	1	0				true	false	false	false
                40072	2	I_AC_Current	AC-Strom Gesamtstromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40076'])			true	false	false	false
                40073	2	I_AC_CurrentA	AC-Strom Phase A (L1) Stromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40076'])			true	false	false	false
                40074	2	I_AC_CurrentB	AC-Strom Phase B (L2) Stromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40076'])			true	false	false	false
                40075	2	I_AC_CurrentC	AC-Strom Phase C (L3) Stromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40076'])			true	false	false	false
                40076	2	I_AC_Current_SF	AC-Strom Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40084	2	I_AC_Power	AC-Leistung Leistungswert	W	int16be	1	1	0	x * Math.pow(10, sf['40085'])			true	false	false	false
                40085	2	I_AC_Power_SF	AC-Leistung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40088	2	I_AC_VA	Scheinleistung	VA	int16be	1	1	0	x * Math.pow(10, sf['40089'])			true	false	false	false
                40089	2	I_AC_VA_SF	Scheinleistung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40090	2	I_AC_VAR	Blindleistung	VAR	int16be	1	1	0	x * Math.pow(10, sf['40091'])			true	false	false	false
                40091	2	I_AC_VAR_SF	Blindleistung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40092	2	I_AC_PF	Leistungsfaktor %	%	int16be	1	1	0	x * Math.pow(10, sf['40093'])			true	false	false	false
                40093	2	I_AC_PF_SF	Leistungsfaktor Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40094	2	I_AC_Energy_WH	AC Energie Gesamt-Energieproduktion	kWh	uint32be	2	1	0	x * Math.pow(10, sf['40096'] - 3)			true	false	false	false
                40096	2	I_AC_Energy_WH_SF	AC Energie Gesamtenergie Skalierungsfaktor	SF	uint16be	1	1	0				true	false	false	true
                40097	2	I_DC_Current	DC-Strom Stromwert	A	uint16be	1	1	0	x * Math.pow(10, sf['40098'])			true	false	false	false
                40098	2	I_DC_Current_SF	DC-Strom Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40099	2	I_DC_Voltage	DC-Spannung Spannungswert	V	uint16be	1	1	0	x * Math.pow(10, sf['40100'])			true	false	false	false
                40100	2	I_DC_Voltage_SF	DC-Spannung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40101	2	I_DC_Power	DC-Leistung Leistungswert	W	int16be	1	1	0	x * Math.pow(10, sf['40102'])			true	false	false	false
                40102	2	I_DC_Power_SF	DC-Leistung Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40104	2	I_Temp_Sink	Kühlkörpertemperatur	°C	int16be	1	1	0	x * Math.pow(10, sf['40107'])			true	false	false	false
                40107	2	I_Temp_SF	Kühlkörpertemperatur Skalierungsfaktor	SF	int16be	1	1	0				true	false	false	true
                40108	2	I_Status	Betriebszustand (1 = Aus, 2 = Schlafen (Automatisches Herunterfahren) – Nachtmodus, 3 = Aufwachen/Starten, 4 = Wechselrichter ist AN und wandelt Energie, 5 = Begrenzte Produktion, 6 = Herunterfahren, 7 = Fehler, 8 = Wartung/Setup)		uint16be	1	1	0				true	false	false	false
                40109	2	I_Status_Vendor	Anbieter-spezifischer Betriebszustand sowie Fehlercodes: 1 = Aus, 2 = Schlafen (Automatisches Herunterfahren) – Nachtmodus, 3 = Aufwachen/Starten, 4 = Wechselrichter ist AN und wandelt Energie, 5 = Begrenzte Produktion, 6 = Herunterfahren, 7 = Fehler, 8 = Wartung/Setup		uint16be	1	1	0				true	false	false	false
                

                Ich danke schonmal im Voraus,
                Apfel

                1 1 Reply Last reply Reply Quote 0
                • 1
                  150d @Apfel85 last edited by

                  @apfel85 Hallo,

                  woher hast Du denn die Adressen für den Batteriespeicher (97600 und folgende?)

                  Ich kannte bisher nur die Adressen aus dem offiziellen Dokument von SolarEdge, in dem die Batterie aber fehlt.

                  Was die Sprünge angeht: In Deiner Tabelle werden konstante Skalierungswerte (z.B. "x * 10^(-3)") verwendet. Bist Du sicher, daß das stimmt? Im Bereich des Inverters sind die Scale Factors nicht konstant, sondern ändern sich dynamisch. Wenn dies im Batterie-Bereich ähnlich ist, würde das die Sprünge erklären.

                  MfG

                  1 Reply Last reply Reply Quote 0
                  • A
                    Apfel85 last edited by Apfel85

                    Guten Abend,

                    ja ich bin mir mit den Adressen relativ sicher. Diese stammen auch aus dem offiziellen SolarEdge Dokument siehe Anhang Power-Control-Open-Protocol-for-SolarEdge-Inverters.pdf

                    Nur musste ich hier ein paar Modifikationen vornehmen. Die original Adressen funktionieren bei mir nicht. Daher habe ich 1. alle Adressen +40000 gerechnet und anschließend nochmals +1 für Base1. Warum das so ist - keine Ahnung. Aber es tut.

                    Zu deinen Fragen - zunächst nochmals Danke für die Unterstützung - Leider finde ich auch zu diesen Werten keinen Scalefactor. Meine Rechnung basiert lediglich darauf, dass aus Wh -> kWh errechnet werden. Ich arbeite lieber damit.

                    Ich habe mir mal den Spaß erlaubt und eine Datenbank die letzten Tage mitlaufen lassen. Aus den Ergebnissen werde ich auch nicht schlüssig...
                    Die letzten 24h hier zu sehen.
                    in BLAU: TotalExport in kWh
                    in Magenta: TotalImport in kWh
                    Screenshot 2023-07-23 223727.jpg
                    Installiert ist ein 13,8 kWh Speicher. Das Ganze läuft nu auch schon >1 Monat. Schlau werde ich leider auch mit verschiedenen Denkansätzen hier nicht....

                    Greetz,
                    Apfel

                    1 1 Reply Last reply Reply Quote 0
                    • 1
                      150d @Apfel85 last edited by

                      @apfel85 Ok, zuerst einmal: Vielen Dank, das Dokument kannte ich noch nicht.

                      Ich habe die Werte inzwischen bei mir eingegeben. Das gleiche Ergebnis wie bei Dir: Max. Temp bleibt Null, die Werte für TotalImport/TotalExport sind unplausibel.

                      Sorry, da weiß ich dann leider auch nicht mehr. 😉

                      Fogg 1 Reply Last reply Reply Quote 0
                      • Fogg
                        Fogg @150d last edited by

                        Mich auch mal hier anhängen... 😄

                        Ich würde gerne von meinem SolarEdge Se16k Daten abfragen. Soweit ich oben sehe geht das nur mit zusätzlichem Zähler? Ist das immernoch so oder kann ich den direkt ansteuern? Im Netz hängt er ja.

                        (Langfristig suche ich noch einen passenden Akku.. .aber denke das ist eher für ein anderes Forum)

                        Glasfaser 1 Reply Last reply Reply Quote 0
                        • Glasfaser
                          Glasfaser @Fogg last edited by Glasfaser

                          @fogg sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                          Soweit ich oben sehe geht das nur mit zusätzlichem Zähler?

                          Nein , du kannst den WR auch ohne Zähler abfragen ,
                          dann fehlen halt nur die Zähler im Modbus Register.

                          1 Reply Last reply Reply Quote 1
                          • M
                            M1R0O last edited by

                            Hi zusammen,
                            ich habe mir den Thread mindestens 1000x durchgelesen...
                            Ich nutze das Register von @Sammydk, welches bei mir super läuft.
                            Theoretisch hätte ich gern die aktuelle PV Produktion (wie diese berechnet wird, hat @Longbow ja erklärt: Batterieladung + den Hausverbrauch + den Export addieren und den Import abziehen.

                            Nun zu meinen Fragen:

                            1. Muss ich die Werte aus dem Register noch umrechnen? (Denn dort sind ja bereits Formeln eingetragen)
                            2. Welches sind die Werte im Holding Register für Batterieladung, Hausverbrauch, Export und Import?

                            Sorry, aber mein Brett vorm Kopf ist zu groß 😕

                            Danke

                            Glasfaser 1 Reply Last reply Reply Quote 0
                            • Glasfaser
                              Glasfaser @M1R0O last edited by

                              @m1r0o sagte in [Tutorial] SolarEdge -> Modbus -> ioBroker -> Grafana:

                              ich habe mir den Thread mindestens 1000x durchgelesen..

                              dann aber alles überlesen 😀 😂

                              Muss ich die Werte aus dem Register noch umrechnen?

                              Nein . hast du dir selber beantwortet.

                              Welches sind die Werte im Holding Register für Batterieladung,

                              57716	Battery 1 Instantaneous Power	Batterie momentane Leistung	W	floatsw	2	1	0		value		true	false	false	false
                              

                              weiteres dazu siehe ein paaaar Antworten über deine Frage !

                              Hausverbrauch, Export und Import?

                              Zitat :

                              Für den Wert 40206: Total Real Power legt ihr folgendes JS Script an:
                              ...4.
                              Stat Import/Export
                              Quelle aus der InfluxDB sind
                              ACTotalRealPower

                              steht alles am Anfang !

                              J 1 Reply Last reply Reply Quote 0
                              • J
                                jumbo125 @Glasfaser last edited by

                                Hallo
                                ich bin zufällig auf das Thema gestoßen und finde es wirklich interessant!!!!!

                                Ich hätte eine Frage zu euren Erfahrungen. Leider habe ich es zuspät gesehen. Daher habe ich es anders gelöst.
                                iobroker->PHP-script->erhält daten, berechnet + speichert in MySql -> grafana visualisierung

                                es funktioniert soweit recht gut. ABER zwei Dinge finde ich komisch

                                1. ALLE WERTE welche ich auslese sind kumulativ. Damit meine ich das ich keine werte mit "Heute erzeugt erhalte".... die Werte werden bei mir alle immer nur weitergezählt.
                                  Daher erhalte ich auch bei 40206 eine unglaublich hohe Zahl. Ist das bei euch auch der Fall?????

                                2. Ich berechne mir immer den Bedarf aus dem Netz, daher kann ich auch täglich den Zählerstand theoretisch berechnen. Dieser Stimmt aber leide nicht überein. ist das bei euch auch der fall?
                                  Die Werte welche ich berechne, stimmen aber mit der APP bis aufs Komma überein

                                T 1 Reply Last reply Reply Quote 0
                                • T
                                  technikaffin @jumbo125 last edited by

                                  @jumbo125

                                  Naja wenn Du den Tageswert haben willst, kannst Du Dir den ja aus dem kumulativen ausrechnen, um 23:59 Uhr

                                  javascript_zeitplan.jpg

                                  AC Gesamt kommt dann vom Wechselrichter kumulativ, die anderen 2 Variablen legst Du Dir selber an. Funktioniert prima bei mir.

                                  J 1 Reply Last reply Reply Quote 0
                                  • J
                                    jumbo125 @technikaffin last edited by

                                    @technikaffin danke dir
                                    dachte bei euch kommen die werte vom WR.
                                    ich habe es bereits bei mir mittels php script geändert, da ich ja auch die daten in eine mysql DB schreibe. es hat mich nur interessiert
                                    danke

                                    1 Reply Last reply Reply Quote 0
                                    • Centurytt 0
                                      Centurytt 0 @hennerich last edited by

                                      @hennerich

                                      Warum berechnest du nicht die Werte gleich im Modbus dann sparst dir das in den Scripten.

                                      ich mache das so z.B.:
                                      ab538379-cbeb-4a5f-a0ea-b793d73dc569-image.png

                                      ist zwar Ansichtssache aber dann habe ich weniger Fehleranfälligkeit und iob hat nicht zig Scripte zum abarbeiten.

                                      Lg
                                      Tom

                                      H 1 Reply Last reply Reply Quote 1
                                      • S
                                        SentiQ last edited by SentiQ

                                        Hat jemand mit Speicher das Problem der aktuellen PV-Leistung irgendwie lösen können? @Glasfaser ich habe zwar deine Scripte integriert mit PVAktuell_ohneSpeicher und PVAktuell_Dachfläche, jedoch habe ich alle paar Minute Werte von paar wenigen Watt und nachts auch mal größere. Sollte ja eigentlich alles auf 0 bleiben von Sonnenuntergang bis Sonnenaufgang.

                                        Beispiel von 2:13 Uhr nachts:

                                        Bildschirmfoto 2023-08-10 um 07.32.32.png

                                        Centurytt 0 1 Reply Last reply Reply Quote 0
                                        • Centurytt 0
                                          Centurytt 0 @SentiQ last edited by

                                          @sentiq

                                          hab auch einen Speicher hab das Problem aber nicht. Ich gehe wie folgt vor:

                                          52d3ebef-15ea-479f-9734-dde008b0c358-image.png

                                          Ich hatte das Problem ganz am Anfang mal als ich das Blockly noch auf vorher berechnete Einzelwerte hatte. Dann war teilweise einfach der iob zu langsam um zu rechnen. Da kam es dann vor, dass die Werte der Batterie als PV Leistung angezeigt wurden. Nachdem ich die MODBUS Berechnungen direkt im Adapter mache und mit den Werten dann rechne ist das nicht mehr passiert.

                                          S 1 Reply Last reply Reply Quote 0
                                          • M
                                            M1R0O last edited by M1R0O

                                            Moin,
                                            @glasfaser: Danke für deine Antwort vor einiger Zeit.

                                            Die Aktuelle PV-Produktion bekomme ich einfach nicht hin!

                                            Centurytt 0 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate

                                            1.0k
                                            Online

                                            31.7k
                                            Users

                                            79.7k
                                            Topics

                                            1.3m
                                            Posts

                                            grafana modbus solaredge
                                            90
                                            603
                                            148442
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo