      gmt94 @Schneider last edited by

      @schneider

      Die ganzen Einsen sind falsch. Also zwischen Adress und Name, die müssen raus.

      1 Reply Last reply Reply Quote 1
      • B
        berlinerbolle @Schneider last edited by

        @schneider
        @gmt94

        Falsch sind die Einsen nicht per se - ich würde empfehlen, die drin zu lassen. Dafür muss aber im Modbus Adapter in den Einstellungen "Multiple Device IDs" angehakt sein, sonst klappt es nicht.

        Vorteil dabei: man kann die einzelnen Batteriewerte per Modbus auslesen, die Batterie hat eine eigene Modbus Adresse.

        Siehe hier.

        G 1 Reply Last reply Reply Quote 1
        • G
          GombersIOB @berlinerbolle last edited by GombersIOB

          @berlinerbolle
          Zumindest ist offensichtlich, dass die Tabelle derzeit nicht zu den Überschriften passt. Ob es eine Einstellung gibt, die der Tabelle eine weitere Spalte hinzufügt, weiß ich nicht. Aber derzeit passen die Einsen jedenfalls nicht rein. Die „Unit“-Werte der Einfügungen werden offensichtlich, wie auch die Fehlermeldung sagt in der Spalte „type“ eingefügt - und entsprechen deshalb nicht den hinterlegten, erlaubten, Werten.
          Die Einsen sind hier und jetzt jedenfalls zu viel.

          B 1 Reply Last reply Reply Quote 0
          • B
            berlinerbolle @GombersIOB last edited by

            @gombersiob

            Vollkommen richtig, so wie es im Screenshot ist, kann es nicht funktionieren - egal ob die Option "Multiple Device IDs" angehakt ist oder nicht. Mit der angehakten Option kommt eine zusätzliche Spalte "deviceId" dazu, die natürlich in der ersten Zeile entsprechend dabei sein muss.

            Deshalb mein Verweis auf das github Repo, da passt es.

            1 Reply Last reply Reply Quote 0
            • S
              Schneider last edited by

              Cool, hat geklappt. Danke für die Hilfe.

              Jetzt habe ich die Objekte drin - allerdings stehen alle auf "0":
              a4b10fb1-3774-4db6-9b3f-a4f98ee6fcd5-grafik.png

              Homoran 1 Reply Last reply Reply Quote 0
              • Homoran
                Homoran Global Moderator Administrators @Schneider last edited by Homoran

                @schneider sagte in Sungrow WR SGH10RT erfolgreich mit MODBUS eingebunden:

                Jetzt habe ich die Objekte drin

                nicht wirklich.
                Da steht bestimmt was im log.

                Das NaN statt Registernummer spricht Bände

                Wo befindest du dich da?

                1 Reply Last reply Reply Quote 0
                • S
                  Schneider last edited by

                  Protokolle:
                  74673d34-2cea-471a-b23b-d6f8d5414dcb-grafik.png

                  Objekte:
                  8a782a8c-d17d-4344-bff9-80509a889d4e-grafik.png

                  Homoran G 2 Replies Last reply Reply Quote 0
                  • Homoran
                    Homoran Global Moderator Administrators @Schneider last edited by Homoran

                    @schneider ... und die Konfiguration?

                    1 Reply Last reply Reply Quote 0
                    • S
                      Schneider last edited by

                      1122bba9-becf-4213-871b-69b9234e8fe7-grafik.png
                      0f27b8cc-4a5f-44e6-b548-df076c1689dd-grafik.png

                      Diskrete Eingänge / Ausgänge habe ich nichts eingetragen. Ebenso ins Holding-Register.

                      ubecker Homoran 2 Replies Last reply Reply Quote 0
                      • ubecker
                        ubecker @Schneider last edited by

                        @schneider nimm mal in der Config Aliasse benutzen raus. Ich erinnere mich das hatte ich auch mal so

                        1 Reply Last reply Reply Quote 0
                        • Homoran
                          Homoran Global Moderator Administrators @Schneider last edited by

                          @schneider bitte Logstufe auf debug umstellen.
                          Hak mal "aliases benutzen" ab

                          1 Reply Last reply Reply Quote 0
                          • S
                            Schneider last edited by

                            Jetzt verbindet sich der Adapter nicht mehr
                            c13de487-ad73-4bdb-a51b-c0978d609dc8-grafik.png

                            c037154c-2b1c-4ecb-bce1-44919358488f-grafik.png

                            Homoran B G 3 Replies Last reply Reply Quote 0
                            • Homoran
                              Homoran Global Moderator Administrators @Schneider last edited by Homoran

                              @schneider sagte in Sungrow WR SGH10RT erfolgreich mit MODBUS eingebunden:

                              Jetzt verbindet sich der Adapter nicht mehr

                              log bitte als Text in code-tags posten und auf debug umstellen

                              EDIT:
                              Wo komnt jetzt due Geräte ID 200 und doppelt so hohe Register her?

                              1 Reply Last reply Reply Quote 0
                              • B
                                berlinerbolle @Schneider last edited by berlinerbolle

                                @schneider

                                Und nimm zur Sicherheit erstmal die Zeilen mit DeviceID 200 (das ist die für den Akku mit den entsprechenden Modbus Registern) ganz raus. Die DeviceID des Akkus MUSS nicht 200 sein (kann man zum Beispiel über das WinetS nachschauen), falls du überhaupt einen hast? Bin gerade am Handy und kann nicht zu deinem ersten Post schauen, welchen Wechselrichter und/oder Akku du hast.

                                Ältere Firmware Versionen führen den Akku auch gar nicht separat auf, das könnte auch eine Ursache sein auch falls du einen Akku hast.

                                1 Reply Last reply Reply Quote 0
                                • G
                                  gmt94 @Schneider last edited by

                                  @schneider

                                  Hast du im Winet dongel überhaupt modbus aktiviert?

                                  S 1 Reply Last reply Reply Quote 0
                                  • G
                                    GombersIOB @Schneider last edited by

                                    @schneider
                                    Diese „Not-a-Number (NaN)“ beziehen sich auf die Registernummern. Da steht in der Spalte sicher noch ein Leerzeichen dabei. Etwa „4999 „ statt „4999“.

                                    Homoran 1 Reply Last reply Reply Quote 0
                                    • Homoran
                                      Homoran Global Moderator Administrators @GombersIOB last edited by

                                      @gombersiob sagte in Sungrow WR SGH10RT erfolgreich mit MODBUS eingebunden:

                                      @schneider
                                      Diese „Not-a-Number (NaN)“ beziehen sich auf die Registernummern. Da steht in der Spalte sicher noch ein Leerzeichen dabei. Etwa „4999 „ statt „4999“.

                                      Das Thema hatten wir gerade erst
                                      https://forum.iobroker.net/post/1221502

                                      Deswegen warte ich auch noch auf das debug-log von @schneider

                                      1 Reply Last reply Reply Quote 0
                                      • S
                                        Schneider last edited by

                                        2024-12-13 19:51:04.877 - info: host.iobroker "system.adapter.modbus.0" enabled
                                        2024-12-13 19:51:05.060 - info: host.iobroker instance system.adapter.modbus.0 in version "6.3.2" started with pid 1511
                                        2024-12-13 19:51:05.555 - debug: modbus.0 (1511) Redis Objects: Use Redis connection: 127.0.0.1:9001
                                        2024-12-13 19:51:05.565 - debug: modbus.0 (1511) Objects client ready ... initialize now
                                        2024-12-13 19:51:05.607 - debug: modbus.0 (1511) Objects create System PubSub Client
                                        2024-12-13 19:51:05.608 - debug: modbus.0 (1511) Objects create User PubSub Client
                                        2024-12-13 19:51:05.618 - debug: modbus.0 (1511) Objects client initialize lua scripts
                                        2024-12-13 19:51:05.620 - debug: modbus.0 (1511) Objects connected to redis: 127.0.0.1:9001
                                        2024-12-13 19:51:05.628 - debug: modbus.0 (1511) Redis States: Use Redis connection: 127.0.0.1:9000
                                        2024-12-13 19:51:05.672 - debug: modbus.0 (1511) States create System PubSub Client
                                        2024-12-13 19:51:05.672 - debug: modbus.0 (1511) States create User PubSub Client
                                        2024-12-13 19:51:05.719 - debug: modbus.0 (1511) States connected to redis: 127.0.0.1:9000
                                        2024-12-13 19:51:05.733 - debug: modbus.0 (1511) Plugin sentry Initialize Plugin (enabled=true)
                                        2024-12-13 19:51:05.919 - info: modbus.0 (1511) starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.19.0, js-controller: 7.0.3
                                        2024-12-13 19:51:05.972 - debug: modbus.0 (1511) Initialize Objects for disInputs: []
                                        2024-12-13 19:51:05.972 - debug: modbus.0 (1511) Initialize Objects for coils: []
                                        2024-12-13 19:51:05.973 - debug: modbus.0 (1511) Initialize Objects for inputRegs: [{"_address":4999,"deviceId":1,"name":"Device type code","description":"Geräte Typ-Code","unit":"","type":"int8be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":4999,"id":"inputRegisters.1.4999_Device_type__code"},{"_address":5000,"deviceId":1,"name":"Nominal Output Power","description":"Installierte Leistung","unit":"Kw","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5000,"id":"inputRegisters.1.5000_Nominal_Output_Power"},{"_address":5002,"deviceId":1,"name":"Daily Output Energy","description":"Eigene Energienutzung heute (PV & Akku)","unit":"Kwh","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5002,"id":"inputRegisters.1.5002_Daily__Output_Energy"},{"_address":5003,"deviceId":1,"name":"Total Output Energy","description":"Eigene Energienutzung gesamt (PV & Akku)","unit":"Kwh","type":"uint32sw","len":2,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5003,"id":"inputRegisters.1.5003_Total_Output_Energy"},{"_address":5007,"deviceId":1,"name":"Inside Temperature","description":"Temperatur im Wechselrichter","unit":"°C","type":"int16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5007,"id":"inputRegisters.1.5007_Inside__Temperature"},{"_address":5010,"deviceId":1,"name":"MPPT 1 Voltage","description":"MPPT1 Spannung","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5010,"id":"inputRegisters.1.5010_MPPT_1_Voltage"},{"_address":5011,"deviceId":1,"name":"MPPT 1 Current","description":"MPPT1 Strom","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5011,"id":"inputRegisters.1.5011_MPPT_1_Current"},{"_address":5012,"deviceId":1,"name":"MPPT 2 Voltage","description":"MPPT2 Spannung","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5012,"id":"inputRegisters.1.5012_MPPT_2_Voltage"},{"_address":5013,"deviceId":1,"name":"MPPT 2 Current","description":"MPPT2 Strom","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5013,"id":"inputRegisters.1.5013_MPPT_2_Current"},{"_address":5016,"deviceId":1,"name":"Total DC Power","description":"PV-Leistung aktuell","unit":"W","type":"uint32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5016,"id":"inputRegisters.1.5016_Total_DC_Power"},{"_address":5018,"deviceId":1,"name":"Spannung Ph A","description":"Spannung Phase A","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5018,"id":"inputRegisters.1.5018_Spannung_Ph_A"},{"_address":5019,"deviceId":1,"name":"Spannung Ph B","description":"Spannung Phase B","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5019,"id":"inputRegisters.1.5019_Spannung_Ph_B"},{"_address":5020,"deviceId":1,"name":"Spannung Ph C","description":"Spannung Phase C","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5020,"id":"inputRegisters.1.5020_Spannung_Ph_C"},{"_address":5032,"deviceId":1,"name":"Reactive Power","description":"Blindleistung","unit":"VA®","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5032,"id":"inputRegisters.1.5032_Reactive_Power"},{"_address":5034,"deviceId":1,"name":"Power Factor","description":"Leistungsfaktor","unit":"","type":"int16be","len":1,"factor":0.001,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5034,"id":"inputRegisters.1.5034_Power_Factor"},{"_address":5035,"deviceId":1,"name":"Grid Frequency","description":"Netzfrequenz","unit":"Hz","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5035,"id":"inputRegisters.1.5035_Grid_Frequency"},{"_address":5600,"deviceId":1,"name":"Gesamtleistung DTSU666","description":"Leistung","unit":"W","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5600,"id":"inputRegisters.1.5600_Gesamtleistung_DTSU666"},{"_address":5602,"deviceId":1,"name":"L1 Leistung DTSU666","description":"Leistung L1","unit":"W","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5602,"id":"inputRegisters.1.5602_L1_Leistung_DTSU666"},{"_address":5604,"deviceId":1,"name":"L2 Leistung DTSU666","description":"Leistung L2","unit":"W","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5604,"id":"inputRegisters.1.5604_L2_Leistung_DTSU666"},{"_address":5606,"deviceId":1,"name":"L3 Leistung DTSU666","description":"Leistung L3","unit":"W","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5606,"id":"inputRegisters.1.5606_L3_Leistung_DTSU666"},{"_address":5740,"deviceId":1,"name":"PhaseA Voltage DTSU666","description":"Spannung Phase1","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5740,"id":"inputRegisters.1.5740_PhaseA_Voltage_DTSU666"},{"_address":5741,"deviceId":1,"name":"PhaseB Voltage DTSU666","description":"Spannung Phase2","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5741,"id":"inputRegisters.1.5741_PhaseB_Voltage_DTSU666"},{"_address":5742,"deviceId":1,"name":"PhaseC Voltage DTSU666","description":"Spannung Phase3","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5742,"id":"inputRegisters.1.5742_PhaseC_Voltage_DTSU666"},{"_address":5743,"deviceId":1,"name":"PhaseA Current DTSU666","description":"Strom Phase1","unit":"A","type":"uint16be","len":1,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5743,"id":"inputRegisters.1.5743_PhaseA_Current_DTSU666"},{"_address":5744,"deviceId":1,"name":"PhaseB Current DTSU666","description":"Strom Phase2","unit":"A","type":"uint16be","len":1,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5744,"id":"inputRegisters.1.5744_PhaseB_Current_DTSU666"},{"_address":5745,"deviceId":1,"name":"PhaseC Current DTSU666","description":"Strom Phase3","unit":"A","type":"uint16be","len":1,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5745,"id":"inputRegisters.1.5745_PhaseC_Current_DTSU666"},{"_address":5746,"deviceId":1,"name":"Import DTSU666","description":"Import","unit":"kWh","type":"uint32sw","len":2,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5746,"id":"inputRegisters.1.5746_Import_DTSU666"},{"_address":5748,"deviceId":1,"name":"Export DTSU666","description":"Export","unit":"kWh","type":"uint32sw","len":2,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5748,"id":"inputRegisters.1.5748_Export_DTSU666"},{"_address":6226,"deviceId":1,"name":"Monthly PV energy yields January","description":" Monatlicher PV Energieertrag Januar","unit":"Kwh","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":6226,"id":"inputRegisters.1.6226_Monthly_PV_energy_yields_January"},{"_address":6227,"deviceId":1,"name":"Monthly PV energy yields February","description":" Monatlicher PV Energieertrag Februar","unit":"Kwh","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":6227,"id":"inputRegisters.1.6227_Monthly_PV_energy_yields_February"},{"_address":6228,"deviceId":1,"name":"Monthly PV energy yields March","description":" Monatlicher PV Energieertrag März","unit":"Kwh","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":6228,"id":"inputRegisters.1.6228_Monthly_PV_energy_yields_March"},
                                        ... GEKÜRZT
                                        {"_id":"inputRegisters.1.13075_BMS_fault_2","type":"state","common":{"name":"BMS fault 2","role":"value","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":13075,"deviceId":1,"type":"uint32sw","len":2,"offset":0,"factor":1}}
                                        2024-12-13 19:51:05.981 - debug: modbus.0 (1511) Add inputRegisters.1.13077_BMS_alarm_2: {"_id":"inputRegisters.1.13077_BMS_alarm_2","type":"state","common":{"name":"BMS alarm 2","role":"value","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":13077,"deviceId":1,"type":"uint32sw","len":2,"offset":0,"factor":1}}
                                        2024-12-13 19:51:05.981 - debug: modbus.0 (1511) Initialize Objects for holdingRegs: []
                                        2024-12-13 19:51:06.325 - info: modbus.0 (1511) Connected to slave 192.168.178.74
                                        2024-12-13 19:51:06.325 - debug: modbus.0 (1511) [DevID_1] Poll start ---------------------
                                        2024-12-13 19:51:06.326 - debug: modbus.0 (1511) Initialization of scale factors done!
                                        2024-12-13 19:51:06.326 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 4999 - 22 registers
                                        2024-12-13 19:51:06.337 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 4999 DONE
                                        2024-12-13 19:51:06.342 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5032 - 4 registers
                                        2024-12-13 19:51:06.346 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5032 DONE
                                        2024-12-13 19:51:06.347 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5600 - 8 registers
                                        2024-12-13 19:51:06.353 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5600 DONE
                                        2024-12-13 19:51:06.356 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5740 - 10 registers
                                        2024-12-13 19:51:06.361 - warn: modbus.0 (1511) [DevID_1] Poll error count: 1 code: "ReadInputRegisters: Invalid FC 132"
                                        2024-12-13 19:51:07.412 - debug: modbus.0 (1511) [DevID_1] Poll start ---------------------
                                        2024-12-13 19:51:07.412 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 4999 - 22 registers
                                        2024-12-13 19:51:07.416 - warn: modbus.0 (1511) Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                                        2024-12-13 19:51:12.613 - warn: modbus.0 (1511) [DevID_1] Poll error count: 2 code: "App Timeout"
                                        2024-12-13 19:51:13.664 - debug: modbus.0 (1511) [DevID_1] Poll start ---------------------
                                        2024-12-13 19:51:13.665 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 4999 - 22 registers
                                        2024-12-13 19:51:18.666 - warn: modbus.0 (1511) Error: undefined
                                        2024-12-13 19:51:18.666 - error: modbus.0 (1511) Request timed out.
                                        2024-12-13 19:51:18.666 - error: modbus.0 (1511) Client in error state.
                                        2024-12-13 19:51:18.666 - warn: modbus.0 (1511) [DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                                        2024-12-13 19:51:18.667 - debug: modbus.0 (1511) Socket closed with error
                                        2024-12-13 19:51:18.667 - debug: modbus.0 (1511) Clearing timeout of the current request.
                                        2024-12-13 19:51:18.667 - debug: modbus.0 (1511) Cleaning up request fifo.
                                        2024-12-13 19:51:19.667 - debug: modbus.0 (1511) Closing client on purpose.
                                        2024-12-13 19:51:19.667 - info: modbus.0 (1511) Disconnected from slave 192.168.178.74
                                        
                                        1 Reply Last reply Reply Quote 0
                                        • S
                                          Schneider @gmt94 last edited by

                                          @gmt94 Ne.. Ich wüsste auch nicht wo. Ist mir zumindest nicht ins Auge gesprungen

                                          G 1 Reply Last reply Reply Quote 0
                                          • G
                                            gmt94 @Schneider last edited by

                                            @schneider

                                            Mal die IP Adresse vom wechselrichter im Browser eintippen und dann per admin anmelden. Passwort sollte in den Unterlagen stehen, dann unter System und weitergabekonfiguration Modus aktivieren.

                                            Screenshot_20241213_202229_Chrome.jpg

                                            1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate
                                            FAQ Cloud / IOT
                                            HowTo: Node.js-Update
                                            HowTo: Backup/Restore
                                            Downloads
                                            BLOG

                                            1.0k
                                            Online

                                            31.6k
                                            Users

                                            79.4k
                                            Topics

                                            1.3m
                                            Posts

                                            hardware sungrow sgh10rt modbu
                                            130
                                            857
                                            247399
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo