      GombersIOB @Schneider last edited by

      @schneider
      Diese „Not-a-Number (NaN)“ beziehen sich auf die Registernummern. Da steht in der Spalte sicher noch ein Leerzeichen dabei. Etwa „4999 „ statt „4999“.

      Homoran 1 Reply Last reply Reply Quote 0
      • Homoran
        Homoran Global Moderator Administrators @GombersIOB last edited by

        @gombersiob sagte in Sungrow WR SGH10RT erfolgreich mit MODBUS eingebunden:

        @schneider
        Diese „Not-a-Number (NaN)“ beziehen sich auf die Registernummern. Da steht in der Spalte sicher noch ein Leerzeichen dabei. Etwa „4999 „ statt „4999“.

        Das Thema hatten wir gerade erst
        https://forum.iobroker.net/post/1221502

        Deswegen warte ich auch noch auf das debug-log von @schneider

        1 Reply Last reply Reply Quote 0
        • S
          Schneider last edited by

          2024-12-13 19:51:04.877 - info: host.iobroker "system.adapter.modbus.0" enabled
          2024-12-13 19:51:05.060 - info: host.iobroker instance system.adapter.modbus.0 in version "6.3.2" started with pid 1511
          2024-12-13 19:51:05.555 - debug: modbus.0 (1511) Redis Objects: Use Redis connection: 127.0.0.1:9001
          2024-12-13 19:51:05.565 - debug: modbus.0 (1511) Objects client ready ... initialize now
          2024-12-13 19:51:05.607 - debug: modbus.0 (1511) Objects create System PubSub Client
          2024-12-13 19:51:05.608 - debug: modbus.0 (1511) Objects create User PubSub Client
          2024-12-13 19:51:05.618 - debug: modbus.0 (1511) Objects client initialize lua scripts
          2024-12-13 19:51:05.620 - debug: modbus.0 (1511) Objects connected to redis: 127.0.0.1:9001
          2024-12-13 19:51:05.628 - debug: modbus.0 (1511) Redis States: Use Redis connection: 127.0.0.1:9000
          2024-12-13 19:51:05.672 - debug: modbus.0 (1511) States create System PubSub Client
          2024-12-13 19:51:05.672 - debug: modbus.0 (1511) States create User PubSub Client
          2024-12-13 19:51:05.719 - debug: modbus.0 (1511) States connected to redis: 127.0.0.1:9000
          2024-12-13 19:51:05.733 - debug: modbus.0 (1511) Plugin sentry Initialize Plugin (enabled=true)
          2024-12-13 19:51:05.919 - info: modbus.0 (1511) starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v18.19.0, js-controller: 7.0.3
          2024-12-13 19:51:05.972 - debug: modbus.0 (1511) Initialize Objects for disInputs: []
          2024-12-13 19:51:05.972 - debug: modbus.0 (1511) Initialize Objects for coils: []
          2024-12-13 19:51:05.973 - debug: modbus.0 (1511) Initialize Objects for inputRegs: [{"_address":4999,"deviceId":1,"name":"Device type code","description":"Geräte Typ-Code","unit":"","type":"int8be","len":1,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":4999,"id":"inputRegisters.1.4999_Device_type__code"},{"_address":5000,"deviceId":1,"name":"Nominal Output Power","description":"Installierte Leistung","unit":"Kw","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5000,"id":"inputRegisters.1.5000_Nominal_Output_Power"},{"_address":5002,"deviceId":1,"name":"Daily Output Energy","description":"Eigene Energienutzung heute (PV & Akku)","unit":"Kwh","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5002,"id":"inputRegisters.1.5002_Daily__Output_Energy"},{"_address":5003,"deviceId":1,"name":"Total Output Energy","description":"Eigene Energienutzung gesamt (PV & Akku)","unit":"Kwh","type":"uint32sw","len":2,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5003,"id":"inputRegisters.1.5003_Total_Output_Energy"},{"_address":5007,"deviceId":1,"name":"Inside Temperature","description":"Temperatur im Wechselrichter","unit":"°C","type":"int16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5007,"id":"inputRegisters.1.5007_Inside__Temperature"},{"_address":5010,"deviceId":1,"name":"MPPT 1 Voltage","description":"MPPT1 Spannung","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5010,"id":"inputRegisters.1.5010_MPPT_1_Voltage"},{"_address":5011,"deviceId":1,"name":"MPPT 1 Current","description":"MPPT1 Strom","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5011,"id":"inputRegisters.1.5011_MPPT_1_Current"},{"_address":5012,"deviceId":1,"name":"MPPT 2 Voltage","description":"MPPT2 Spannung","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5012,"id":"inputRegisters.1.5012_MPPT_2_Voltage"},{"_address":5013,"deviceId":1,"name":"MPPT 2 Current","description":"MPPT2 Strom","unit":"A","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5013,"id":"inputRegisters.1.5013_MPPT_2_Current"},{"_address":5016,"deviceId":1,"name":"Total DC Power","description":"PV-Leistung aktuell","unit":"W","type":"uint32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5016,"id":"inputRegisters.1.5016_Total_DC_Power"},{"_address":5018,"deviceId":1,"name":"Spannung Ph A","description":"Spannung Phase A","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5018,"id":"inputRegisters.1.5018_Spannung_Ph_A"},{"_address":5019,"deviceId":1,"name":"Spannung Ph B","description":"Spannung Phase B","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5019,"id":"inputRegisters.1.5019_Spannung_Ph_B"},{"_address":5020,"deviceId":1,"name":"Spannung Ph C","description":"Spannung Phase C","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5020,"id":"inputRegisters.1.5020_Spannung_Ph_C"},{"_address":5032,"deviceId":1,"name":"Reactive Power","description":"Blindleistung","unit":"VA®","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5032,"id":"inputRegisters.1.5032_Reactive_Power"},{"_address":5034,"deviceId":1,"name":"Power Factor","description":"Leistungsfaktor","unit":"","type":"int16be","len":1,"factor":0.001,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5034,"id":"inputRegisters.1.5034_Power_Factor"},{"_address":5035,"deviceId":1,"name":"Grid Frequency","description":"Netzfrequenz","unit":"Hz","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5035,"id":"inputRegisters.1.5035_Grid_Frequency"},{"_address":5600,"deviceId":1,"name":"Gesamtleistung DTSU666","description":"Leistung","unit":"W","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5600,"id":"inputRegisters.1.5600_Gesamtleistung_DTSU666"},{"_address":5602,"deviceId":1,"name":"L1 Leistung DTSU666","description":"Leistung L1","unit":"W","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5602,"id":"inputRegisters.1.5602_L1_Leistung_DTSU666"},{"_address":5604,"deviceId":1,"name":"L2 Leistung DTSU666","description":"Leistung L2","unit":"W","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5604,"id":"inputRegisters.1.5604_L2_Leistung_DTSU666"},{"_address":5606,"deviceId":1,"name":"L3 Leistung DTSU666","description":"Leistung L3","unit":"W","type":"int32sw","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5606,"id":"inputRegisters.1.5606_L3_Leistung_DTSU666"},{"_address":5740,"deviceId":1,"name":"PhaseA Voltage DTSU666","description":"Spannung Phase1","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5740,"id":"inputRegisters.1.5740_PhaseA_Voltage_DTSU666"},{"_address":5741,"deviceId":1,"name":"PhaseB Voltage DTSU666","description":"Spannung Phase2","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5741,"id":"inputRegisters.1.5741_PhaseB_Voltage_DTSU666"},{"_address":5742,"deviceId":1,"name":"PhaseC Voltage DTSU666","description":"Spannung Phase3","unit":"V","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5742,"id":"inputRegisters.1.5742_PhaseC_Voltage_DTSU666"},{"_address":5743,"deviceId":1,"name":"PhaseA Current DTSU666","description":"Strom Phase1","unit":"A","type":"uint16be","len":1,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5743,"id":"inputRegisters.1.5743_PhaseA_Current_DTSU666"},{"_address":5744,"deviceId":1,"name":"PhaseB Current DTSU666","description":"Strom Phase2","unit":"A","type":"uint16be","len":1,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5744,"id":"inputRegisters.1.5744_PhaseB_Current_DTSU666"},{"_address":5745,"deviceId":1,"name":"PhaseC Current DTSU666","description":"Strom Phase3","unit":"A","type":"uint16be","len":1,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5745,"id":"inputRegisters.1.5745_PhaseC_Current_DTSU666"},{"_address":5746,"deviceId":1,"name":"Import DTSU666","description":"Import","unit":"kWh","type":"uint32sw","len":2,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5746,"id":"inputRegisters.1.5746_Import_DTSU666"},{"_address":5748,"deviceId":1,"name":"Export DTSU666","description":"Export","unit":"kWh","type":"uint32sw","len":2,"factor":0.01,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":5748,"id":"inputRegisters.1.5748_Export_DTSU666"},{"_address":6226,"deviceId":1,"name":"Monthly PV energy yields January","description":" Monatlicher PV Energieertrag Januar","unit":"Kwh","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":6226,"id":"inputRegisters.1.6226_Monthly_PV_energy_yields_January"},{"_address":6227,"deviceId":1,"name":"Monthly PV energy yields February","description":" Monatlicher PV Energieertrag Februar","unit":"Kwh","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":6227,"id":"inputRegisters.1.6227_Monthly_PV_energy_yields_February"},{"_address":6228,"deviceId":1,"name":"Monthly PV energy yields March","description":" Monatlicher PV Energieertrag März","unit":"Kwh","type":"uint16be","len":1,"factor":0.1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":6228,"id":"inputRegisters.1.6228_Monthly_PV_energy_yields_March"},
          ... GEKÜRZT
          {"_id":"inputRegisters.1.13075_BMS_fault_2","type":"state","common":{"name":"BMS fault 2","role":"value","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":13075,"deviceId":1,"type":"uint32sw","len":2,"offset":0,"factor":1}}
          2024-12-13 19:51:05.981 - debug: modbus.0 (1511) Add inputRegisters.1.13077_BMS_alarm_2: {"_id":"inputRegisters.1.13077_BMS_alarm_2","type":"state","common":{"name":"BMS alarm 2","role":"value","type":"number","read":true,"write":false,"def":0,"unit":""},"native":{"regType":"inputRegs","address":13077,"deviceId":1,"type":"uint32sw","len":2,"offset":0,"factor":1}}
          2024-12-13 19:51:05.981 - debug: modbus.0 (1511) Initialize Objects for holdingRegs: []
          2024-12-13 19:51:06.325 - info: modbus.0 (1511) Connected to slave 192.168.178.74
          2024-12-13 19:51:06.325 - debug: modbus.0 (1511) [DevID_1] Poll start ---------------------
          2024-12-13 19:51:06.326 - debug: modbus.0 (1511) Initialization of scale factors done!
          2024-12-13 19:51:06.326 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 4999 - 22 registers
          2024-12-13 19:51:06.337 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 4999 DONE
          2024-12-13 19:51:06.342 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5032 - 4 registers
          2024-12-13 19:51:06.346 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5032 DONE
          2024-12-13 19:51:06.347 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5600 - 8 registers
          2024-12-13 19:51:06.353 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5600 DONE
          2024-12-13 19:51:06.356 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 5740 - 10 registers
          2024-12-13 19:51:06.361 - warn: modbus.0 (1511) [DevID_1] Poll error count: 1 code: "ReadInputRegisters: Invalid FC 132"
          2024-12-13 19:51:07.412 - debug: modbus.0 (1511) [DevID_1] Poll start ---------------------
          2024-12-13 19:51:07.412 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 4999 - 22 registers
          2024-12-13 19:51:07.416 - warn: modbus.0 (1511) Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
          2024-12-13 19:51:12.613 - warn: modbus.0 (1511) [DevID_1] Poll error count: 2 code: "App Timeout"
          2024-12-13 19:51:13.664 - debug: modbus.0 (1511) [DevID_1] Poll start ---------------------
          2024-12-13 19:51:13.665 - debug: modbus.0 (1511) [DevID_1/inputRegs] Poll address 4999 - 22 registers
          2024-12-13 19:51:18.666 - warn: modbus.0 (1511) Error: undefined
          2024-12-13 19:51:18.666 - error: modbus.0 (1511) Request timed out.
          2024-12-13 19:51:18.666 - error: modbus.0 (1511) Client in error state.
          2024-12-13 19:51:18.666 - warn: modbus.0 (1511) [DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
          2024-12-13 19:51:18.667 - debug: modbus.0 (1511) Socket closed with error
          2024-12-13 19:51:18.667 - debug: modbus.0 (1511) Clearing timeout of the current request.
          2024-12-13 19:51:18.667 - debug: modbus.0 (1511) Cleaning up request fifo.
          2024-12-13 19:51:19.667 - debug: modbus.0 (1511) Closing client on purpose.
          2024-12-13 19:51:19.667 - info: modbus.0 (1511) Disconnected from slave 192.168.178.74
          
          1 Reply Last reply Reply Quote 0
          • S
            Schneider @gmt94 last edited by

            @gmt94 Ne.. Ich wüsste auch nicht wo. Ist mir zumindest nicht ins Auge gesprungen

            G 1 Reply Last reply Reply Quote 0
            • G
              gmt94 @Schneider last edited by

              @schneider

              Mal die IP Adresse vom wechselrichter im Browser eintippen und dann per admin anmelden. Passwort sollte in den Unterlagen stehen, dann unter System und weitergabekonfiguration Modus aktivieren.

              Screenshot_20241213_202229_Chrome.jpg

              1 Reply Last reply Reply Quote 0
              • S
                Schneider last edited by

                Das ist/war an:cc63a1c9-7f2d-4437-b578-2510610f65ee-grafik.png

                Weiß jemand was das für ne Fehlermeldung im Log ist?
                "ReadInputRegisters: Invalid FC 132"

                B 1 Reply Last reply Reply Quote 0
                • S
                  Schneider last edited by Schneider

                  Interessant.. ich hab n Gläschen Wein getrunken, nichts verändert und nun siehts so aus:2d3b8413-966d-4903-a951-a432960c14bf-grafik.png

                  und gleich danach wieder nicht mehr verbunden:
                  3862fc11-aa01-4e9f-92db-e7cb4d373910-grafik.png

                  2024-12-13 23:14:54.608 - info: modbus.0 (1839) Connected to slave 192.168.178.74
                  2024-12-13 23:14:54.608 - debug: modbus.0 (1839) [DevID_1] Poll start ---------------------
                  2024-12-13 23:14:54.608 - debug: modbus.0 (1839) [DevID_1/inputRegs] Poll address 4999 - 22 registers
                  2024-12-13 23:14:59.609 - warn: modbus.0 (1839) Error: undefined
                  2024-12-13 23:14:59.609 - error: modbus.0 (1839) Request timed out.
                  2024-12-13 23:14:59.609 - error: modbus.0 (1839) Client in error state.
                  2024-12-13 23:14:59.609 - warn: modbus.0 (1839) [DevID_1] Poll error count: 4 code: {"err":"timeout","timeout":5000}
                  2024-12-13 23:14:59.610 - debug: modbus.0 (1839) Socket closed with error
                  2024-12-13 23:14:59.610 - debug: modbus.0 (1839) Clearing timeout of the current request.
                  2024-12-13 23:14:59.610 - debug: modbus.0 (1839) Cleaning up request fifo.
                  2024-12-13 23:15:00.610 - debug: modbus.0 (1839) Closing client on purpose.
                  2024-12-13 23:15:00.610 - info: modbus.0 (1839) Disconnected from slave 192.168.178.74
                  2024-12-13 23:16:00.614 - info: modbus.0 (1839) Connected to slave 192.168.178.74
                  2024-12-13 23:16:00.614 - debug: modbus.0 (1839) [DevID_1] Poll start ---------------------
                  2024-12-13 23:16:00.614 - debug: modbus.0 (1839) [DevID_1/inputRegs] Poll address 4999 - 22 registers
                  2024-12-13 23:16:05.615 - warn: modbus.0 (1839) Error: undefined
                  2024-12-13 23:16:05.615 - error: modbus.0 (1839) Request timed out.
                  2024-12-13 23:16:05.615 - error: modbus.0 (1839) Client in error state.
                  2024-12-13 23:16:05.615 - warn: modbus.0 (1839) [DevID_1] Poll error count: 5 code: {"err":"timeout","timeout":5000}
                  2024-12-13 23:16:05.616 - debug: modbus.0 (1839) Socket closed with error
                  2024-12-13 23:16:05.616 - debug: modbus.0 (1839) Clearing timeout of the current request.
                  2024-12-13 23:16:05.616 - debug: modbus.0 (1839) Cleaning up request fifo.
                  2024-12-13 23:16:06.616 - debug: modbus.0 (1839) Closing client on purpose.
                  2024-12-13 23:16:06.616 - info: modbus.0 (1839) Disconnected from slave 192.168.178.74
                  2024-12-13 23:16:07.424 - info: influxdb.0 (418) enabled logging of modbus.0.inputRegisters.1.5600_Gesamtleistung_DTSU666, Alias=false
                  2024-12-13 23:17:06.620 - info: modbus.0 (1839) Connected to slave 192.168.178.74
                  2024-12-13 23:17:06.620 - debug: modbus.0 (1839) [DevID_1] Poll start ---------------------
                  2024-12-13 23:17:06.620 - debug: modbus.0 (1839) [DevID_1/inputRegs] Poll address 4999 - 22 registers
                  2024-12-13 23:17:11.621 - warn: modbus.0 (1839) Error: undefined
                  2024-12-13 23:17:11.621 - error: modbus.0 (1839) Request timed out.
                  2024-12-13 23:17:11.621 - error: modbus.0 (1839) Client in error state.
                  2024-12-13 23:17:11.622 - warn: modbus.0 (1839) [DevID_1] Poll error count: 6 code: {"err":"timeout","timeout":5000}
                  2024-12-13 23:17:11.622 - debug: modbus.0 (1839) Socket closed with error
                  2024-12-13 23:17:11.622 - debug: modbus.0 (1839) Clearing timeout of the current request.
                  2024-12-13 23:17:11.622 - debug: modbus.0 (1839) Cleaning up request fifo.
                  2024-12-13 23:17:12.622 - debug: modbus.0 (1839) Closing client on purpose.
                  2024-12-13 23:17:12.622 - info: modbus.0 (1839) Disconnected from slave 192.168.178.74
                  
                  B 1 Reply Last reply Reply Quote 0
                  • B
                    berlinerbolle @Schneider last edited by

                    Mal ganz blöd gefragt, hat denn jemand erfolgreich einen WR vom gleichen Typ wie @Schneider ihn hat, eingebunden? Und falls ja, mit welchen Registern?

                    Die Fehlermeldung "Invalid FC 132" klingt für mich nach einer ungültigen Registeradresse.

                    Ich würde jetzt alle Register rausschmeißen, und nur ein einziges drin lassen - dann schauen ob es geht. Falls ja, nach und nach die gewünschten Register hinzufügen. Die Registeradressen sind zwischen den verschiedenen WR nicht unbedingt identisch. Es gibt da auch (unvollständige) Dokumentation von Sungrow dazu.

                    G 1 Reply Last reply Reply Quote 0
                    • B
                      berlinerbolle @Schneider last edited by

                      @schneider

                      Hast Du mal das Abfrageintervall verlängert? Eine Sekunde ist ziemlich stramm für den WR. Ich hab da zum Beispiel drei Sekunden drin stehen.

                      1 Reply Last reply Reply Quote 0
                      • S
                        Schneider last edited by Schneider

                        Danke für die Tipps. ICh glaube so gehts.
                        Ich habe jetzt nur die drin gelassen, die eben einen Wert gebracht haben, sowie das Abfrageintervall auf 3s.

                        Jetzt werden die Werte auch aktualisiert. Super cool. Danke für die Unterstützung!
                        2c08330f-8089-411d-a375-e6f2440dd66c-grafik.png

                        Ergänzend:

                        _address	deviceId	name	description	unit	type	len	factor	offset	formula	role	room	cw	isScale
                        4999	1	Device type  code	Geräte Typ-Code		int8be	1	1	0		value		false	false
                        5000	1	Nominal Output Power	Installierte Leistung	Kw	uint16be	1	0.1	0		value		false	false
                        5002	1	Daily  Output Energy	Eigene Energienutzung heute (PV & Akku)	Kwh	uint16be	1	0.1	0		value		false	false
                        5003	1	Total Output Energy	Eigene Energienutzung gesamt (PV & Akku)	Kwh	uint32sw	2	0.1	0		value		false	false
                        5007	1	Inside  Temperature	Temperatur im Wechselrichter	°C	int16be	1	0.1	0		value		false	false
                        5010	1	MPPT 1 Voltage	MPPT1 Spannung	V	uint16be	1	0.1	0		value		false	false
                        5011	1	MPPT 1 Current	MPPT1 Strom	A	uint16be	1	0.1	0		value		false	false
                        5012	1	MPPT 2 Voltage	MPPT2 Spannung	V	uint16be	1	0.1	0		value		false	false
                        5013	1	MPPT 2 Current	MPPT2 Strom	A	uint16be	1	0.1	0		value		false	false
                        5016	1	Total DC Power	PV-Leistung aktuell	W	uint32sw	2	1	0		value		false	false
                        5018	1	Spannung Ph A	Spannung Phase A	V	uint16be	1	0.1	0		value		false	false
                        5019	1	Spannung Ph B	Spannung Phase B	V	uint16be	1	0.1	0		value		false	false
                        5020	1	Spannung Ph C	Spannung Phase C	V	uint16be	1	0.1	0		value		false	false
                        5032	1	Reactive Power	Blindleistung	VA®	int32sw	2		0		value		false	false
                        5034	1	Power Factor	Leistungsfaktor		int16be	1	0.001	0		value		false	false
                        5035	1	Grid Frequency	Netzfrequenz	Hz	uint16be	1	0.1	0		value		false	false
                        5600	1	Gesamtleistung DTSU666	Leistung	W	int32sw	2	1	0		value		false	false
                        5602	1	L1 Leistung DTSU666	Leistung L1	W	int32sw	2	1	0		value		false	false
                        5604	1	L2 Leistung DTSU666	Leistung L2	W	int32sw	2	1	0		value		false	false
                        5606	1	L3 Leistung DTSU666	Leistung L3	W	int32sw	2	1	0		value		false	false
                        
                        1 Reply Last reply Reply Quote 0
                        • G
                          GombersIOB @berlinerbolle last edited by GombersIOB

                          @berlinerbolle
                          Solange er die Register nicht korrigiert, wird das nichts werden.

                          Die Aufrufbarkeit des Wechselrichters kann er mit eine Modbus-Client, die es frei zu laden gibt, testen. Ich verwende dafür "VagaModbus Analyzer", er ist simpel und intuitiv zu bedienen

                          Das hat sich mit dem vorigen Post überschnitten - jetzt scheint es ja zu funktionieren.

                          1 Reply Last reply Reply Quote 0
                          • S
                            Schneider last edited by

                            Ja, mit einigen Werten aus github gehts - leider nicht alle.

                            Und die Batterie geht auch nicht.
                            cb050a3c-aac3-4395-b9c4-9e45259d42c2-grafik.png

                            467a23ad-ffc2-45ad-bc67-486a7dba048e-grafik.png

                            1 Reply Last reply Reply Quote 0
                            • S
                              Schneider last edited by

                              Okay.. die ID ist nicht die 200, sondern die 2.
                              Ist im WiNet-S2 auch toll beschrieben mit Modus-ID (statt Modbus-ID):
                              478d2043-dec2-4919-86f0-397389574a28-grafik.png

                              B Homoran 2 Replies Last reply Reply Quote 0
                              • B
                                berlinerbolle @Schneider last edited by

                                @schneider

                                Ja, das meinte ich weiter oben - es muss nicht unbedingt die 200 sein (bei mir war es die 200, deshalb auch so auf GitHub hinterlegt).

                                Aber top dass es jetzt läuft!

                                1 Reply Last reply Reply Quote 0
                                • Homoran
                                  Homoran Global Moderator Administrators @Schneider last edited by Homoran

                                  @schneider sagte in Sungrow WR SGH10RT erfolgreich mit MODBUS eingebunden:

                                  die ID ist nicht die 200, sondern die 2.

                                  und daher kam der FC132

                                  daher auch meine Nachfrage
                                  @homoran sagte in Sungrow WR SGH10RT erfolgreich mit MODBUS eingebunden:

                                  EDIT:
                                  Wo komnt jetzt die Geräte ID 200 und doppelt so hohe Register her?

                                  Ein einziger Fehleintrag lähmt den ganzen Bus
                                  Man fängt daher immer nur mit einer Adresse/Gerät an zu testen.
                                  Dann Stück für Stück erweitern.

                                  1 Reply Last reply Reply Quote 0
                                  • L
                                    luxusl last edited by

                                    Hallo zusammen,

                                    ich hab einen SH10RT und einen SG7.0 Wechselrichter im Retrofit-Modus.

                                    Die Darstellung des Hausverbrauches will bei mir einfach nicht passen...
                                    Über Modbus lese ich die AC Wirkleistung von beiden Wechselrichtern aus (#5030) und addiere diese zzgl. 140W, allerdings ist es nicht der korrekte Wert für den in der App dargestellten Wert. Natürlich sind die Werte in der App etwas zeitversetzt, aber bei mir ist die zeitliche Abweichung gering. Jemand eine Idee was ich hier falsch mache?

                                    1.JPG 2.JPG

                                    1 Reply Last reply Reply Quote 0
                                    • D
                                      DRUROB last edited by

                                      Hallo!

                                      Ich habe die Problematik, dass die Werte für die Batterieladeleistung überhaupt nicht mehr passen.
                                      Ich kann euch nicht mal genau sagen seit wann der Fehler da ist....
                                      Im register 13021 stehen immer Werte (also falls der Ladevorgang aktiv ist) um die 64.000 (tausend) drin. Im Register 13020 für die Ampere sind ebenfalls nur 64.000er Werte vorhanden, allerdings ist ja hier in der Grundkonfig bereits ein Faktor 0.1 hinterlegt. Daher denke ich das das Grundproblem aus den 13020 herkommt und er intern die Ladeleistung aus 13019 und 13020 berechnet. Ich habe die Einstellungen konntrolliert aber die sind immer noch die gleichen wie bei allen Eingangsregistertabellen die ich hier im Forum finden konnte. Type "Unsigned 16bit (Big Endian)
                                      Oder hat sich das irgendwie geändert?
                                      Im Sungrow gab es keine Umstellung die ich nicht mitbekommen habe?

                                      VG!

                                      W 1 Reply Last reply Reply Quote 0
                                      • W
                                        wolfi913 @DRUROB last edited by

                                        @drurob

                                        Im Sungrow gab es keine Umstellung die ich nicht mitbekommen habe?

                                        Könnte sein das Sungrow da an der Firmware gedreht hat.
                                        Bei mir passen die Modbus-Register (noch).

                                        Aber bei evcc findet sich dazu auch schon was in der Richtung:
                                        https://github.com/evcc-io/evcc/issues/18270
                                        Möglicherweise hilft das ja weiter.

                                        Bluppy created this issue in evcc-io/evcc

                                        closed Sungrow SH15 Batterie Ladung wird nicht erkannt. #18270

                                        D 1 Reply Last reply Reply Quote 0
                                        • D
                                          DRUROB @wolfi913 last edited by

                                          @wolfi913 Danke, ich habe mir das mal kurz überflogen. tatsächlich gab es wohl eine neue Firmware. Ich schau mal ob ich die schon bekommen habe .... Grüße!

                                          1 Reply Last reply Reply Quote 0
                                          • D
                                            DRUROB last edited by DRUROB

                                            Tatsächlich gab es ein Update....na super.
                                            Nachdem ich mich nun ewig nicht damit beschäftigt habe und auch glücklicherweise nicht musste, habe ich ich natürlich jetzt ganz schön Nachholbedarf.

                                            Bei meiner Einrichtung damals waren die Register für Batterie und Smartmeter noch gar kein Thema.
                                            Jetzt wo ich schon mal bei bin möchte ich die ebenfalls einpflegen, aber....
                                            Ich such wie doof aber in den derzeit angebotenen Dateien finden sich die Register aber nicht.
                                            Kann mir jemand bitte die Dateien geben wo drin ich die Angaben zu den verfügbaren Registern für Batterie und Smartmeter finde? ich würde dann die Dateien zusammenführen und hier wieder rein posten, dann hat es der nächste vielleicht etwas leichter.

                                            Ich ärgere mich etwas darüber den Post mit den Angaben nicht gespeichert zu haben, aber ich hoffe wir finden den gemeinsam wieder....

                                            EDIT:
                                            wer suchet der findet..... was man nicht im Kopf hat.......
                                            https://github.com/c0ldtech/sungrow/blob/main/sungrow_input_registers_multiple_IDs.tsv

                                            M 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate
                                            FAQ Cloud / IOT
                                            HowTo: Node.js-Update
                                            HowTo: Backup/Restore
                                            Downloads
                                            BLOG

                                            689
                                            Online

                                            31.7k
                                            Users

                                            79.8k
                                            Topics

                                            1.3m
                                            Posts

                                            hardware sungrow sgh10rt modbu
                                            130
                                            860
                                            279405
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo