      Thomas P 0 @Homoran last edited by

      @homoran
      Die Request-Message passt. Allerdings erwartet der Zähler gemäß IEC62056-21 nach der Request-Message noch das ACK-Signal und das was er machen soll, in dem Fall den String 0Z0 CR+LF. Dann kommen die Daten. Aber so wie ich das Log lesen, sendet das smarmeter-Adapter nur den Anfang /?! CR+LF
      1a9f2d5d-250d-4635-af05-cccfce5eee5c-image.png
      Und da auf Github "Mode 😄 baudrate changeover and Ack-Message needed" habe ich auch damals das Überschreiben der Baudrate-Änderung auf 300 gesetzt, und Mode C ausgewäht. Baud-Rate stimmt, nur die "Acknowledgement/option select message" fehlt noch. Die sendet der smartmeter-Adapter nicht.

      Homoran wendy2702 apollon77 3 Replies Last reply Reply Quote 0
      • T
        Thomas P 0 @Homoran last edited by

        @homoran
        Aus https://www.counttec.de/WebRoot/Store26/Shops/17782539/57CE/96DE/FA76/51DB/2B0B/C0A8/2ABA/7B8B/Bedienungsanleitung_Drehstromzaehler_Counttec_Baylan.pdf

        Aus dem Thread https://forum.iobroker.net/topic/62395/baylan-drehstromzähler-erfahrung/2

        1 Reply Last reply Reply Quote 0
        • Homoran
          Homoran Global Moderator Administrators @Thomas P 0 last edited by

          @thomas-p-0 da müsste jetzt @apollon77 was zu sagen. Das geht mir zu tief.

          1 Reply Last reply Reply Quote 0
          • wendy2702
            wendy2702 @Thomas P 0 last edited by

            @thomas-p-0 Hatte es eben schon geschrieben aber hast du mal nur Mode A oder C ausgewählt ohne die Baudrate anzugeben?

            T 1 Reply Last reply Reply Quote 0
            • T
              Thomas P 0 @wendy2702 last edited by Thomas P 0

              @wendy2702
              Mode C ja, Mode A nein, teste gerade. Sieht aber genau so aus wie bei Mode C. Mode A sendet wenn ich es richtig gelesen habe ja kein ACK

              P.S.: Mode A macht das selbe

              1 Reply Last reply Reply Quote 0
              • apollon77
                apollon77 @SuperDa last edited by

                @superda Versuch es doch mal mit mbus ... und ganz ehrlich ... Frag ggf echt beim Hersteller

                1 Reply Last reply Reply Quote 0
                • apollon77
                  apollon77 @Thomas P 0 last edited by

                  @thomas-p-0 Muss ichmir später mal anschauen ... An sich sendet der Adapter alles automatisch ... Keine Ahnung was der Zähler wieder spezielles hat

                  T 1 Reply Last reply Reply Quote 0
                  • T
                    Thomas P 0 @apollon77 last edited by

                    @apollon77
                    Naja, spezielles eigentlich nicht, es steht ja so in der Norm.

                    Falls du Zugang brauchst zum Livesystem sag bescheid, dann schalte ich ssh frei. Http braucht leider etwas zum Feischalten, das muss ich mir morgen mal anschauen.

                    apollon77 1 Reply Last reply Reply Quote 0
                    • apollon77
                      apollon77 @Thomas P 0 last edited by

                      @thomas-p-0 bitte Screenshot der konfig und vollständiges debug log posten nichts weglassen wie oben (da hast du am Anfang was nicht dabei)

                      T 1 Reply Last reply Reply Quote 0
                      • T
                        Thomas P 0 @apollon77 last edited by

                        @apollon77
                        Hallo Apollon,
                        2793b27c-0ff0-4b3f-a313-5eb9adfd4936-image.png

                        2023-02-04 19:45:51.562  - info: host.zaehlerpi stopInstance system.adapter.smartmeter.0 (force=false, process=true)
                        2023-02-04 19:45:51.574  - info: smartmeter.0 (3434) Got terminate signal TERMINATE_YOURSELF
                        2023-02-04 19:45:51.578  - debug: smartmeter.0 (3434) STOP
                        2023-02-04 19:45:51.580  - debug: smartmeter.0 (3434) CLEAR MESSAGE TIMEOUT TIMER
                        2023-02-04 19:45:51.582  - info: smartmeter.0 (3434) terminating
                        2023-02-04 19:45:51.585  - debug: smartmeter.0 (3434) Plugin sentry destroyed
                        2023-02-04 19:45:51.586  - info: smartmeter.0 (3434) Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                        2023-02-04 19:45:51.613  - info: host.zaehlerpi stopInstance system.adapter.smartmeter.0 send kill signal
                        2023-02-04 19:45:52.177  - info: host.zaehlerpi instance system.adapter.smartmeter.0 terminated with code 11 (ADAPTER_REQUESTED_TERMINATION)
                        2023-02-04 19:45:54.674  - info: host.zaehlerpi instance system.adapter.smartmeter.0 started with pid 5793
                        2023-02-04 19:45:58.307  - debug: smartmeter.0 (5793) Redis Objects: Use Redis connection: 127.0.0.1:9001
                        2023-02-04 19:45:58.446  - debug: smartmeter.0 (5793) Objects client ready ... initialize now
                        2023-02-04 19:45:58.454  - debug: smartmeter.0 (5793) Objects create System PubSub Client
                        2023-02-04 19:45:58.459  - debug: smartmeter.0 (5793) Objects create User PubSub Client
                        2023-02-04 19:45:58.550  - debug: smartmeter.0 (5793) Objects client initialize lua scripts
                        2023-02-04 19:45:58.577  - debug: smartmeter.0 (5793) Objects connected to redis: 127.0.0.1:9001
                        2023-02-04 19:45:58.628  - debug: smartmeter.0 (5793) Redis States: Use Redis connection: 127.0.0.1:9000
                        2023-02-04 19:45:58.649  - debug: smartmeter.0 (5793) States create System PubSub Client
                        2023-02-04 19:45:58.654  - debug: smartmeter.0 (5793) States create User PubSub Client
                        2023-02-04 19:45:58.681  - debug: smartmeter.0 (5793) States connected to redis: 127.0.0.1:9000
                        2023-02-04 19:45:58.744  - debug: smartmeter.0 (5793) Plugin sentry Initialize Plugin (enabled=true)
                        2023-02-04 19:45:59.335  - info: smartmeter.0 (5793) starting. Version 3.3.4 in /opt/iobroker/node_modules/iobroker.smartmeter, node: v16.19.0, js-controller: 4.0.24
                        2023-02-04 19:45:59.403  - debug: smartmeter.0 (5793) SmartmeterObis options: {"debug":2,"protocol":"D0Protocol","transport":"SerialRequestResponseTransport","requestInterval":"300","anotherQueryDelay":"1000","transportSerialPort":"/dev/serial/by-id/usb-Silicon_Labs_CP2102_USB_to_UART_Bridge_Controller_0041-if00-port0","transportSerialBaudrate":null,"transportSerialMessageTimeout":null,"protocolD0WakeupCharacters":0,"protocolD0DeviceAddress":"66002067","obisFallbackMedium":1}
                        2023-02-04 19:45:59.411  - debug: smartmeter.0 (5793) CREATE SERIALPORT: 300 7 1 even
                        2023-02-04 19:45:59.431  - debug: smartmeter.0 (5793) SERIALPORT OPEN
                        2023-02-04 19:45:59.470  - debug: smartmeter.0 (5793) SERIALPORT RESET BAUDRATE TO 300
                        2023-02-04 19:45:59.479  - debug: smartmeter.0 (5793) INITIAL MESSAGES TO SEND: 2
                        2023-02-04 19:45:59.482  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 0 IN GETNEXTMESSAGE
                        2023-02-04 19:45:59.484  - debug: smartmeter.0 (5793) TO SEND 2:
                        2023-02-04 19:45:59.485  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 1 IN GETNEXTMESSAGE
                        2023-02-04 19:45:59.487  - debug: smartmeter.0 (5793) TO SEND 1: /?66002067!
                        
                        2023-02-04 19:45:59.519  - debug: smartmeter.0 (5793) connected set to false
                        2023-02-04 19:45:59.896  - debug: smartmeter.0 (5793) DONE SEND 1
                        2023-02-04 19:45:59.958  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:45:59.963  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:45:59.964  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/" -> null
                        2023-02-04 19:45:59.988  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:45:59.990  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:45:59.992  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/B" -> null
                        2023-02-04 19:46:00.022  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.024  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.025  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BY" -> null
                        2023-02-04 19:46:00.055  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.057  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.058  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL" -> null
                        2023-02-04 19:46:00.089  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.091  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.093  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6" -> null
                        2023-02-04 19:46:00.122  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.124  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.126  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<" -> null
                        2023-02-04 19:46:00.150  - debug: smartmeter.0 (5793) DONE SEND 0
                        2023-02-04 19:46:00.154  - debug: smartmeter.0 (5793) SET MESSAGE TIMEOUT TIMER2: 120000
                        2023-02-04 19:46:00.177  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.179  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.181  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1" -> null
                        2023-02-04 19:46:00.192  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.194  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.195  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>" -> null
                        2023-02-04 19:46:00.222  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.224  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.225  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>B" -> null
                        2023-02-04 19:46:00.256  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.257  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.258  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BY" -> null
                        2023-02-04 19:46:00.288  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.289  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.290  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL" -> null
                        2023-02-04 19:46:00.322  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.323  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.324  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-" -> null
                        2023-02-04 19:46:00.355  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.356  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.357  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-C" -> null
                        2023-02-04 19:46:00.388  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.390  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.391  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CR" -> null
                        2023-02-04 19:46:00.423  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.424  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.425  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH" -> null
                        2023-02-04 19:46:00.455  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.456  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.457  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-" -> null
                        2023-02-04 19:46:00.489  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.490  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.491  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-B" -> null
                        2023-02-04 19:46:00.521  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.523  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.524  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-BT" -> null
                        2023-02-04 19:46:00.556  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.558  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.559  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-BTK" -> null
                        2023-02-04 19:46:00.588  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.589  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.590  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-BTK3" -> null
                        2023-02-04 19:46:00.622  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.623  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.624  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-BTK30" -> null
                        2023-02-04 19:46:00.654  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.657  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.658  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-BTK30-" -> null
                        2023-02-04 19:46:00.688  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.690  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.691  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-BTK30-R" -> null
                        2023-02-04 19:46:00.722  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.723  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.725  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-BTK30-R1" -> null
                        2023-02-04 19:46:00.755  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.756  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.757  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-BTK30-R1\r" -> null
                        2023-02-04 19:46:00.789  - debug: smartmeter.0 (5793) NEW DATA
                        2023-02-04 19:46:00.790  - debug: smartmeter.0 (5793) CURRENT PROCESS STEP 2 IN CHECKMESSAGE
                        2023-02-04 19:46:00.791  - debug: smartmeter.0 (5793) MATCH-RESULT SIGNON: "/BYL6<1>BYL-CRH-BTK30-R1\r\n" -> null
                        2023-02-04 19:48:00.159  - debug: smartmeter.0 (5793) MESSAGE TIMEOUT TRIGGERED
                        2023-02-04 19:48:00.162  - debug: smartmeter.0 (5793) Error: No or too long answer from Serial Device after last request.
                        2023-02-04 19:48:00.167  - warn: smartmeter.0 (5793) No or too long answer from Serial Device after last request.
                        2023-02-04 19:48:00.169  - debug: smartmeter.0 (5793) Error: No or too long answer from Serial Device after last request.
                        2023-02-04 19:48:00.170  - debug: smartmeter.0 (5793) Transport Reset!! Restart = true
                        2023-02-04 19:48:00.173  - debug: smartmeter.0 (5793) STOP
                        2023-02-04 19:48:00.174  - debug: smartmeter.0 (5793) CLEAR MESSAGE TIMEOUT TIMER
                        2023-02-04 19:48:00.190  - debug: smartmeter.0 (5793) SERIALPORT CLOSE
                        2023-02-04 19:48:00.192  - debug: smartmeter.0 (5793) SERIALPORT REMOVE LISTENERS
                        2023-02-04 19:48:00.198  - debug: smartmeter.0 (5793) CURRENT SIGNON MESSAGE COUNTER 1 OF 1
                        2023-02-04 19:48:00.200  - debug: smartmeter.0 (5793) DELETE rest of data (0) because new Message start with a new Request Message
                        2023-02-04 19:48:00.201  - debug: smartmeter.0 (5793) SCHEDULE NEXT RUN IN 300000s
                        
                        

                        Das ist ein ganzer Abfragezyklus. Ich habe den Adapter eu gestartet, um die Abfrage auszulösen.

                        MfG
                        Thomas Pfaffinger

                        apollon77 1 Reply Last reply Reply Quote 0
                        • apollon77
                          apollon77 @Thomas P 0 last edited by apollon77

                          @thomas-p-0 warum ist bei Modus override ein C drin? Der Grund ist aktuell das er die signon Nachricht nicht erkennt. Daher geht’s nicht weiter. Mein Tipp liegt an den < Bzw >. Muss schauen was die specs sagen aber solche Zeichen wären mir an sich neu. Dann müsste ich das einbauen. Wenn die Kinderbibel Bett sind schaue ich mal.

                          Edit aaahhhhhhh tja die signon ist zu lang formal … um ein Zeichen zu lang.

                          https://github.com/Apollon77/smartmeter-obis/blob/master/lib/protocols/D0Protocol.js Hier zeile 9 das 4,22 heißt „nach dem / kommen vor dem Zeilenende 4 bis 22 Zeichen“. Dein Zähler senden …. Trommelwirbel …. 23 (wenn ich mich nicht verzählt hab) kannst das file mal suchen und nen 23 reinschreiben anstelle der 22. wenn’s dann weitergeht ist’s das. Dann bitte github issue Anlegen. Muss ich wohl das Limit ändern. Hachja. Standards und die Hersteller …

                          T 1 Reply Last reply Reply Quote 0
                          • T
                            Thomas P 0 @apollon77 last edited by Thomas P 0

                            @apollon77 said in Adapter "smartmeter":

                            D0Protocol.js

                            Guten Morgen Appollon,
                            ja das war es. Jetzt funktioniert es. Vielen Dank. Kann man dir irgendwie ein Dankeschön zukommen lassen?
                            In meinen Spec stehen übrigens 32 Zeichen. Welche ist denn nun richtig? 🙂
                            iec62056-21_en

                            Und ja, das ist der Grund, warum ich in der IT arbeite. Ein Zeichen und schon geht es

                            MfG
                            Thomas Pfaffinger

                            P.S.: Issue ist angelegt. Ich hoffe, das ich das richtig gemacht habe. Ist mein erster

                            apollon77 2 Replies Last reply Reply Quote 0
                            • apollon77
                              apollon77 @Thomas P 0 last edited by

                              @thomas-p-0 na dann lese ich mal deine specs ;-)) vllt gabs ein Update.

                              Zum „zukommen lassen“ ist Link in meinem footer hier im Forum Oder auch im github bei den Adaptern Seite und oben unter „Sponsor“ als begriff. Danke.

                              1 Reply Last reply Reply Quote 0
                              • apollon77
                                apollon77 @Thomas P 0 last edited by

                                @thomas-p-0 ich gehe davon aus das mit der Änderung bei dir erstmal alles tut? Oder geht noch irgendetwas nicht?

                                T 1 Reply Last reply Reply Quote 0
                                • T
                                  Thomas P 0 @apollon77 last edited by

                                  @apollon77
                                  Allo Apollon,
                                  nein, soweit alles perfekt.

                                  MfG
                                  Thomas Pfaffinger

                                  apollon77 1 Reply Last reply Reply Quote 0
                                  • apollon77
                                    apollon77 @Thomas P 0 last edited by

                                    @thomas-p-0 Ok, dann Todo liste 🙂

                                    1 Reply Last reply Reply Quote 0
                                    • M
                                      mirko3107 last edited by

                                      Hallo,

                                      ich habe in meinem Zählerschrank einen "Sagemcom Smarty BZ-Plus" verbaut, einen Zweirichtungszähler.
                                      Aus diesem hatte ich gehofft, die Werte für den aktuellen Verbauch sowie für die einzelnen Phasen per D0
                                      auslesen zu können.
                                      Hab einen USB-IR-Lesekopf an einem Raspberry und einer kleinen Iobroker-Installation als Slave.
                                      Mein erster Erfolg war ein Auslesen per SML, aber da kam nur der aktuelle Verbrauch und ein paar Zählerstände.

                                      Hab dann D0 versucht, da spuckt er mir aber nur Zählerstände aus für jeden Monat des vergangenen Jahres,
                                      keine aktuellen Verbräuche.

                                      Hat noch jemand diesen Zähler erfolgreich auslesen können?
                                      Handbuch1
                                      Handbuch2

                                      Meine Settings:

                                      smarty.JPG

                                      Danke
                                      Mirko

                                      Homoran wendy2702 2 Replies Last reply Reply Quote 0
                                      • Homoran
                                        Homoran Global Moderator Administrators @mirko3107 last edited by

                                        @mirko3107 sagte in Adapter "smartmeter":

                                        Mein erster Erfolg war ein Auslesen per SML, aber da kam nur der aktuelle Verbrauch und ein paar Zählerstände.

                                        das ist dann der richtige Weg gewesen.
                                        Meht gibt es meistens nicht.

                                        1 Reply Last reply Reply Quote 0
                                        • wendy2702
                                          wendy2702 @mirko3107 last edited by

                                          @mirko3107 Im Handbuch 1 Seite 16/17 steht doch genau welche Daten man mit welchem Protokoll abfragen kann.

                                          Mehr geht halt nicht.

                                          1 Reply Last reply Reply Quote 0
                                          • M
                                            mirko3107 last edited by

                                            Wenn ich im Handbuch2 auf Seite 77 lese, hatte ich mir mehr Werte erhofft, aber wenn nicht mehr kommt, nutzt
                                            mir das alles nix.

                                            wendy2702 Homoran 2 Replies Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate
                                            FAQ Cloud / IOT
                                            HowTo: Node.js-Update
                                            HowTo: Backup/Restore
                                            Downloads
                                            BLOG

                                            1.0k
                                            Online

                                            31.6k
                                            Users

                                            79.5k
                                            Topics

                                            1.3m
                                            Posts

                                            279
                                            3620
                                            1715505
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo