    [HowTo] Huawei SUN2000 WR Modbus mit node-red (read + write)

    This topic has been deleted. Only users with topic management privileges can see it.
    • B
      Biervoegelhasso @Murokey last edited by

      @murokey
      Ich dachte mit der Firmenware des Dongles weißt du. Das du dich mit dem Dongle nicht verbinden konntest lag bestimmt an einer zu alten Firmenware. Das Problem hatte ich auch. (The SDongle that needs to be upgraded should have firmware version SDongleV100R001C00SPC115 or later, otherwise the upgrade cannot be performed locally.)
      Der Huawei Support hat dann per Fernwartung ein Update gemacht.

      M 1 Reply Last reply Reply Quote 0
      • M
        Murokey @Biervoegelhasso last edited by Murokey

        Arbeitet ihr allgemein mit Node-red als separater Installation oder mir dem Node-Red Adapter des ioBroker?

        Ich habe Node-red separat installiert und finde irgendwie keine Möglichkeit wie ich die iobroker in und iobroker out nodes herbekomme.

        B 1 Reply Last reply Reply Quote 0
        • B
          badsnoopy667 @Murokey last edited by

          @murokey ich habe den Adapter installiert. Wusste nicht mal, dass das auch anders geht.
          Bisher nutze ich es auch ausschließlich für den Huawei WR. Und dafür funktioniert es einwandfrei.

          1 Reply Last reply Reply Quote 0
          • P
            ple last edited by

            So, ich habe neue Infos, der ktl 30-m3 kann anscheinend kein Modbus TCP mit dem Dongle, es soll angeblich ein Firmware update geben irgendwann mal. Na toll.
            habt ihr alle hier kleinere Modelle vom ktl m3?

            gruß

            M J 2 Replies Last reply Reply Quote 1
            • M
              Murokey @ple last edited by

              @ple
              Ich habe einen 10KLT-M1, dieser wird ja schon mit dem WLAN-FE Dongle ausgeliefert und nach den Startschwierigkeiten bekomme ich jetzt auch die Daten rein.

              1 Reply Last reply Reply Quote 0
              • J
                joeysch @ple last edited by

                @ple
                Also ich habe auch einen KTL30-M3 und es funktioniert mit Node Red.
                Dongle Version 123
                Wechselrichter Version 111
                Die nachfolgenden Versionen hatte ich ausprobiert und dann wieder downgegraded. Ging nicht.
                Hier ist der Flow

                [
                    {
                        "id": "78bcc7b.07aa038",
                        "type": "tab",
                        "label": "Modbus TCP",
                        "disabled": false,
                        "info": ""
                    },
                    {
                        "id": "7f192735.7f04d8",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Interne Temperatur",
                        "topic": "0_userdata.0.Huawei.Inverter.Internal_Temperature",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 730,
                        "y": 1300,
                        "wires": []
                    },
                    {
                        "id": "b1161bcd.470708",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Input Power",
                        "topic": "0_userdata.0.Huawei.Inverter.Input_Power",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 880,
                        "wires": []
                    },
                    {
                        "id": "8b6b24cb.456578",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Peak Active Power of current Day",
                        "topic": "0_userdata.0.Huawei.Inverter.Peak_Active_Power_of_current_Day",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 780,
                        "y": 1060,
                        "wires": []
                    },
                    {
                        "id": "b348383d.407648",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Active Power",
                        "topic": "0_userdata.0.Huawei.Inverter.Active_Power",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 1120,
                        "wires": []
                    },
                    {
                        "id": "ae33615.ef40da",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Efficiency ",
                        "topic": "0_userdata.0.Huawei.Inverter.Efficiency",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 700,
                        "y": 1240,
                        "wires": []
                    },
                    {
                        "id": "fe38cb9c.a4dd68",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Accumulated Energy Yield",
                        "topic": "0_userdata.0.Huawei.Inverter.Accumulated_Energy_Yield",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 750,
                        "y": 1420,
                        "wires": []
                    },
                    {
                        "id": "7ae30e4.55869f",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "PV1 Voltage",
                        "topic": "0_userdata.0.Huawei.Inverter.PV1_Voltage",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 400,
                        "wires": []
                    },
                    {
                        "id": "20f6d52e.26fdfa",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "PV1 Current",
                        "topic": "0_userdata.0.Huawei.Inverter.PV1_Current",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 460,
                        "wires": []
                    },
                    {
                        "id": "e998ba99.a57228",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "PV2 Voltage",
                        "topic": "0_userdata.0.Huawei.Inverter.PV2_Voltage",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 520,
                        "wires": []
                    },
                    {
                        "id": "b67e39ed.028a78",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "PV2 Current",
                        "topic": "0_userdata.0.Huawei.Inverter.PV2_Current",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 580,
                        "wires": []
                    },
                    {
                        "id": "85c06382.4a9b1",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Grid Frequency",
                        "topic": "0_userdata.0.Huawei.Inverter.Grid_Frequency",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "Grid frequency",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "HZ",
                        "stateMin": "0",
                        "stateMax": "60",
                        "x": 720,
                        "y": 1180,
                        "wires": []
                    },
                    {
                        "id": "e8afb02b.08e91",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Insulation Resistance",
                        "topic": "0_userdata.0.Huawei.Inverter.Insulation_Resistance",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 740,
                        "y": 1360,
                        "wires": []
                    },
                    {
                        "id": "a922a727.2c6088",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Daily Energy Yield",
                        "topic": "0_userdata.0.Huawei.Inverter.Daily_Energy_Yield",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 730,
                        "y": 1480,
                        "wires": []
                    },
                    {
                        "id": "e8ec50e.aea08b",
                        "type": "inject",
                        "z": "78bcc7b.07aa038",
                        "name": "10 Sec. Intervall",
                        "props": [
                            {
                                "p": "payload"
                            },
                            {
                                "p": "topic",
                                "vt": "str"
                            }
                        ],
                        "repeat": "10",
                        "crontab": "",
                        "once": true,
                        "onceDelay": "0.1",
                        "topic": "",
                        "payload": "",
                        "payloadType": "date",
                        "x": 130,
                        "y": 160,
                        "wires": [
                            [
                                "6dddc7c0.2b30f8"
                            ]
                        ]
                    },
                    {
                        "id": "3996c271.4a964e",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Power Grid Voltage",
                        "topic": "0_userdata.0.Huawei.Inverter.Power_Grid_Voltage",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 730,
                        "y": 940,
                        "wires": []
                    },
                    {
                        "id": "5a3c69ff.c24f98",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Power Grid Current",
                        "topic": "0_userdata.0.Huawei.Inverter.Power_Grid_Current",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 730,
                        "y": 1000,
                        "wires": []
                    },
                    {
                        "id": "d5a9a6fb.7c5408",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Model",
                        "topic": "0_userdata.0.Huawei.Inverter.Model",
                        "ack": "true",
                        "autoCreate": "true",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 690,
                        "y": 280,
                        "wires": []
                    },
                    {
                        "id": "1f15301e.28c0d",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "Model ID",
                        "topic": "0_userdata.0.Huawei.Inverter.Model_ID",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 700,
                        "y": 340,
                        "wires": []
                    },
                    {
                        "id": "42b5f1fc.28bc1",
                        "type": "comment",
                        "z": "78bcc7b.07aa038",
                        "name": "Daten Wechselrichter",
                        "info": "",
                        "x": 380,
                        "y": 160,
                        "wires": []
                    },
                    {
                        "id": "53a9ec17.8b2fe4",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "PV3 Voltage",
                        "topic": "0_userdata.0.Huawei.Inverter.PV3_Voltage",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 640,
                        "wires": []
                    },
                    {
                        "id": "802eca.72dcd138",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "PV3 Current",
                        "topic": "0_userdata.0.Huawei.Inverter.PV3_Current",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 700,
                        "wires": []
                    },
                    {
                        "id": "7b71d68b.3df2f8",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "PV4 Voltage",
                        "topic": "0_userdata.0.Huawei.Inverter.PV4_Voltage",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 760,
                        "wires": []
                    },
                    {
                        "id": "3f92a0c.5da616",
                        "type": "ioBroker out",
                        "z": "78bcc7b.07aa038",
                        "name": "PV4 Current",
                        "topic": "0_userdata.0.Huawei.Inverter.PV4_Current",
                        "ack": "true",
                        "autoCreate": "false",
                        "stateName": "Huawei",
                        "role": "temperature",
                        "payloadType": "number",
                        "readonly": "true",
                        "stateUnit": "°C",
                        "stateMin": "",
                        "stateMax": "",
                        "x": 710,
                        "y": 820,
                        "wires": []
                    },
                    {
                        "id": "cd15434a.e68f1",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32087",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32087",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 1300,
                        "wires": [
                            [
                                "e5619565.985e28"
                            ],
                            [
                                "7817613d.a127e"
                            ]
                        ]
                    },
                    {
                        "id": "287319c6.b373f6",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32064",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32064",
                        "quantity": "2",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 880,
                        "wires": [
                            [
                                "d2927739.83f298"
                            ],
                            [
                                "3e4a8574.469efa"
                            ]
                        ]
                    },
                    {
                        "id": "3c914caf.5738e4",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32078",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32078",
                        "quantity": "2",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 1060,
                        "wires": [
                            [
                                "f3c37488.7ecae8"
                            ],
                            [
                                "d9bd6742.505968"
                            ]
                        ]
                    },
                    {
                        "id": "d9bd6742.505968",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32080",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32080",
                        "quantity": "2",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 1120,
                        "wires": [
                            [
                                "748cd6be.711418"
                            ],
                            [
                                "267382c6.bb1a8e"
                            ]
                        ]
                    },
                    {
                        "id": "de6e01cf.1babb",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32086",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32086",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 1240,
                        "wires": [
                            [
                                "d1eac20a.fd546"
                            ],
                            [
                                "cd15434a.e68f1"
                            ]
                        ]
                    },
                    {
                        "id": "23a05a60.7a5216",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32106",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32106",
                        "quantity": "2",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 1420,
                        "wires": [
                            [
                                "13c902f0.e19bdd"
                            ],
                            [
                                "1b3aca18.baeaa6"
                            ]
                        ]
                    },
                    {
                        "id": "b900f2aa.29994",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32016",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32016",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 400,
                        "wires": [
                            [
                                "cf006310.a1f2c"
                            ],
                            [
                                "50d53b31.a543e4"
                            ]
                        ]
                    },
                    {
                        "id": "50d53b31.a543e4",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32017",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32017",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 460,
                        "wires": [
                            [
                                "e6804f64.105de"
                            ],
                            [
                                "37582474.3167bc"
                            ]
                        ]
                    },
                    {
                        "id": "37582474.3167bc",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32018",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32018",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 520,
                        "wires": [
                            [
                                "92074916.f988e8"
                            ],
                            [
                                "89b4ae7.006de5"
                            ]
                        ]
                    },
                    {
                        "id": "89b4ae7.006de5",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32019",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32019",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 580,
                        "wires": [
                            [
                                "48b9d754.2bf578"
                            ],
                            [
                                "80a44a9c.347948"
                            ]
                        ]
                    },
                    {
                        "id": "267382c6.bb1a8e",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32085",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32085",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 1180,
                        "wires": [
                            [
                                "635bee76.0254d"
                            ],
                            [
                                "de6e01cf.1babb"
                            ]
                        ]
                    },
                    {
                        "id": "7817613d.a127e",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32088",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32088",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 1360,
                        "wires": [
                            [
                                "f87e60d1.9574e"
                            ],
                            [
                                "23a05a60.7a5216"
                            ]
                        ]
                    },
                    {
                        "id": "1b3aca18.baeaa6",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32114",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32114",
                        "quantity": "2",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 1480,
                        "wires": [
                            [
                                "2172b185.4b630e"
                            ],
                            []
                        ]
                    },
                    {
                        "id": "3e4a8574.469efa",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32066",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32066",
                        "quantity": "2",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 940,
                        "wires": [
                            [
                                "1e1ec634.66e6da"
                            ],
                            [
                                "bbacbb38.8dacb8"
                            ]
                        ]
                    },
                    {
                        "id": "bbacbb38.8dacb8",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32072",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32072",
                        "quantity": "2",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 1000,
                        "wires": [
                            [
                                "1e28c400.529afc"
                            ],
                            [
                                "3c914caf.5738e4"
                            ]
                        ]
                    },
                    {
                        "id": "6dddc7c0.2b30f8",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "30000",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "30000",
                        "quantity": "15",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 280,
                        "wires": [
                            [
                                "c5dccba9.887548"
                            ],
                            [
                                "320bb00e.64185"
                            ]
                        ]
                    },
                    {
                        "id": "320bb00e.64185",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "30070",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "30070",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 340,
                        "wires": [
                            [
                                "23bd63c4.74e6cc"
                            ],
                            [
                                "b900f2aa.29994"
                            ]
                        ]
                    },
                    {
                        "id": "80a44a9c.347948",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32020",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32020",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 640,
                        "wires": [
                            [
                                "d862e633.a8a088"
                            ],
                            [
                                "88f0ea06.ee5ab8"
                            ]
                        ]
                    },
                    {
                        "id": "88f0ea06.ee5ab8",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32021",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32021",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 700,
                        "wires": [
                            [
                                "ecc9586f.339e88"
                            ],
                            [
                                "5345ba59.79f1c4"
                            ]
                        ]
                    },
                    {
                        "id": "5345ba59.79f1c4",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32022",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32022",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 760,
                        "wires": [
                            [
                                "6d68c1b2.8b289"
                            ],
                            [
                                "29d25680.6cc24a"
                            ]
                        ]
                    },
                    {
                        "id": "29d25680.6cc24a",
                        "type": "modbus-getter",
                        "z": "78bcc7b.07aa038",
                        "name": "32023",
                        "showStatusActivities": false,
                        "showErrors": false,
                        "logIOActivities": false,
                        "unitid": "1",
                        "dataType": "HoldingRegister",
                        "adr": "32023",
                        "quantity": "1",
                        "server": "70220ecd.1ca1e",
                        "useIOFile": false,
                        "ioFile": "",
                        "useIOForPayload": false,
                        "emptyMsgOnFail": false,
                        "keepMsgProperties": false,
                        "x": 210,
                        "y": 820,
                        "wires": [
                            [
                                "2f9bb0fb.4096f"
                            ],
                            [
                                "287319c6.b373f6"
                            ]
                        ]
                    },
                    {
                        "id": "d2927739.83f298",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int32be",
                                "name": "Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 880,
                        "wires": [
                            [
                                "af79ce87.b753b"
                            ]
                        ]
                    },
                    {
                        "id": "f3c37488.7ecae8",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int32be",
                                "name": "Rated Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 1060,
                        "wires": [
                            [
                                "20815958.10bdc6"
                            ]
                        ]
                    },
                    {
                        "id": "748cd6be.711418",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int32be",
                                "name": "Active Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 1120,
                        "wires": [
                            [
                                "24604dc3.b7a1a2"
                            ]
                        ]
                    },
                    {
                        "id": "d1eac20a.fd546",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "uint16be",
                                "name": "Wirkungsgrad",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "0.01",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 1240,
                        "wires": [
                            [
                                "ae33615.ef40da"
                            ]
                        ]
                    },
                    {
                        "id": "e5619565.985e28",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "uint16be",
                                "name": "Temperatur",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 1300,
                        "wires": [
                            [
                                "6a77e118.4529e"
                            ]
                        ]
                    },
                    {
                        "id": "13c902f0.e19bdd",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "uint32be",
                                "name": "Meter Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 1420,
                        "wires": [
                            [
                                "def025a8.e64258"
                            ]
                        ]
                    },
                    {
                        "id": "cf006310.a1f2c",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int16be",
                                "name": "Active Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 400,
                        "wires": [
                            [
                                "3b19ffb9.1e7f"
                            ]
                        ]
                    },
                    {
                        "id": "e6804f64.105de",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int16be",
                                "name": "Active Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 460,
                        "wires": [
                            [
                                "2e1aa9d1.aa86a6"
                            ]
                        ]
                    },
                    {
                        "id": "92074916.f988e8",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int16be",
                                "name": "Active Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 520,
                        "wires": [
                            [
                                "7f9a982c.10bd38"
                            ]
                        ]
                    },
                    {
                        "id": "48b9d754.2bf578",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int16be",
                                "name": "Active Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 580,
                        "wires": [
                            [
                                "514b795f.c885d8"
                            ]
                        ]
                    },
                    {
                        "id": "635bee76.0254d",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "uint16be",
                                "name": "Grid frequency",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 1180,
                        "wires": [
                            [
                                "86bd3f2f.22fa2"
                            ]
                        ]
                    },
                    {
                        "id": "f87e60d1.9574e",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "uint16be",
                                "name": "Wirkungsgrad",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "0.001",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 1360,
                        "wires": [
                            [
                                "e8afb02b.08e91"
                            ]
                        ]
                    },
                    {
                        "id": "2172b185.4b630e",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "uint32be",
                                "name": "Meter Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 1480,
                        "wires": [
                            [
                                "a13f1ae4.bda158"
                            ]
                        ]
                    },
                    {
                        "id": "1e1ec634.66e6da",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "uint16be",
                                "name": "Grid Voltage",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 940,
                        "wires": [
                            [
                                "76f4925c.0b90bc"
                            ]
                        ]
                    },
                    {
                        "id": "1e28c400.529afc",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int32be",
                                "name": "Grid current",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 1000,
                        "wires": [
                            [
                                "3b9634ff.c9e3ac"
                            ]
                        ]
                    },
                    {
                        "id": "c5dccba9.887548",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "string",
                                "name": "Model",
                                "offset": 0,
                                "length": 15,
                                "offsetbit": 0,
                                "scale": "0.1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 280,
                        "wires": [
                            [
                                "d5a9a6fb.7c5408"
                            ]
                        ]
                    },
                    {
                        "id": "23bd63c4.74e6cc",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "uint16be",
                                "name": "Model ID",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 340,
                        "wires": [
                            [
                                "1f15301e.28c0d"
                            ]
                        ]
                    },
                    {
                        "id": "d862e633.a8a088",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int16be",
                                "name": "Active Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 640,
                        "wires": [
                            [
                                "4ae79dde.3fcbd4"
                            ]
                        ]
                    },
                    {
                        "id": "ecc9586f.339e88",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int16be",
                                "name": "Active Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 700,
                        "wires": [
                            [
                                "a4a2b892.32cd68"
                            ]
                        ]
                    },
                    {
                        "id": "6d68c1b2.8b289",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int16be",
                                "name": "Active Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 760,
                        "wires": [
                            [
                                "b8f2f270.61bc"
                            ]
                        ]
                    },
                    {
                        "id": "2f9bb0fb.4096f",
                        "type": "buffer-parser",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "data": "payload",
                        "dataType": "msg",
                        "specification": "spec",
                        "specificationType": "ui",
                        "items": [
                            {
                                "type": "int16be",
                                "name": "Active Power",
                                "offset": 0,
                                "length": 1,
                                "offsetbit": 0,
                                "scale": "1",
                                "mask": ""
                            }
                        ],
                        "swap1": "",
                        "swap2": "",
                        "swap3": "",
                        "swap1Type": "swap",
                        "swap2Type": "swap",
                        "swap3Type": "swap",
                        "msgProperty": "payload",
                        "msgPropertyType": "str",
                        "resultType": "value",
                        "resultTypeType": "output",
                        "multipleResult": false,
                        "fanOutMultipleResult": false,
                        "setTopic": true,
                        "outputs": 1,
                        "x": 390,
                        "y": 820,
                        "wires": [
                            [
                                "8306cf5f.45806"
                            ]
                        ]
                    },
                    {
                        "id": "2e1aa9d1.aa86a6",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "100",
                        "round": true,
                        "decimals": "3",
                        "x": 550,
                        "y": 460,
                        "wires": [
                            [
                                "20f6d52e.26fdfa"
                            ]
                        ]
                    },
                    {
                        "id": "514b795f.c885d8",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "100",
                        "round": true,
                        "decimals": "3",
                        "x": 550,
                        "y": 580,
                        "wires": [
                            [
                                "b67e39ed.028a78"
                            ]
                        ]
                    },
                    {
                        "id": "3b19ffb9.1e7f",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "10",
                        "round": true,
                        "decimals": "2",
                        "x": 550,
                        "y": 400,
                        "wires": [
                            [
                                "7ae30e4.55869f"
                            ]
                        ]
                    },
                    {
                        "id": "7f9a982c.10bd38",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "10",
                        "round": true,
                        "decimals": "2",
                        "x": 550,
                        "y": 520,
                        "wires": [
                            [
                                "e998ba99.a57228"
                            ]
                        ]
                    },
                    {
                        "id": "3b9634ff.c9e3ac",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "1000",
                        "round": true,
                        "decimals": "3",
                        "x": 550,
                        "y": 1000,
                        "wires": [
                            [
                                "5a3c69ff.c24f98"
                            ]
                        ]
                    },
                    {
                        "id": "def025a8.e64258",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "100",
                        "round": true,
                        "decimals": "2",
                        "x": 550,
                        "y": 1420,
                        "wires": [
                            [
                                "fe38cb9c.a4dd68"
                            ]
                        ]
                    },
                    {
                        "id": "a13f1ae4.bda158",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "100",
                        "round": true,
                        "decimals": "2",
                        "x": 550,
                        "y": 1480,
                        "wires": [
                            [
                                "a922a727.2c6088"
                            ]
                        ]
                    },
                    {
                        "id": "76f4925c.0b90bc",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "10",
                        "round": true,
                        "decimals": "2",
                        "x": 550,
                        "y": 940,
                        "wires": [
                            [
                                "3996c271.4a964e"
                            ]
                        ]
                    },
                    {
                        "id": "86bd3f2f.22fa2",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "100",
                        "round": true,
                        "decimals": "2",
                        "x": 550,
                        "y": 1180,
                        "wires": [
                            [
                                "85c06382.4a9b1"
                            ]
                        ]
                    },
                    {
                        "id": "6a77e118.4529e",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "10",
                        "round": true,
                        "decimals": "1",
                        "x": 550,
                        "y": 1300,
                        "wires": [
                            [
                                "7f192735.7f04d8"
                            ]
                        ]
                    },
                    {
                        "id": "af79ce87.b753b",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "1",
                        "round": true,
                        "decimals": "0",
                        "x": 550,
                        "y": 880,
                        "wires": [
                            [
                                "b1161bcd.470708"
                            ]
                        ]
                    },
                    {
                        "id": "24604dc3.b7a1a2",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "1",
                        "round": true,
                        "decimals": "0",
                        "x": 550,
                        "y": 1120,
                        "wires": [
                            [
                                "b348383d.407648"
                            ]
                        ]
                    },
                    {
                        "id": "20815958.10bdc6",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "1",
                        "round": true,
                        "decimals": "0",
                        "x": 550,
                        "y": 1060,
                        "wires": [
                            [
                                "8b6b24cb.456578"
                            ]
                        ]
                    },
                    {
                        "id": "a4a2b892.32cd68",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "100",
                        "round": true,
                        "decimals": "3",
                        "x": 550,
                        "y": 700,
                        "wires": [
                            [
                                "802eca.72dcd138"
                            ]
                        ]
                    },
                    {
                        "id": "4ae79dde.3fcbd4",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "10",
                        "round": true,
                        "decimals": "2",
                        "x": 550,
                        "y": 640,
                        "wires": [
                            [
                                "53a9ec17.8b2fe4"
                            ]
                        ]
                    },
                    {
                        "id": "8306cf5f.45806",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "100",
                        "round": true,
                        "decimals": "3",
                        "x": 550,
                        "y": 820,
                        "wires": [
                            [
                                "3f92a0c.5da616"
                            ]
                        ]
                    },
                    {
                        "id": "b8f2f270.61bc",
                        "type": "calculator",
                        "z": "78bcc7b.07aa038",
                        "name": "",
                        "inputMsgField": "payload",
                        "outputMsgField": "payload",
                        "operation": "div",
                        "constant": "10",
                        "round": true,
                        "decimals": "2",
                        "x": 550,
                        "y": 760,
                        "wires": [
                            [
                                "7b71d68b.3df2f8"
                            ]
                        ]
                    },
                    {
                        "id": "70220ecd.1ca1e",
                        "type": "modbus-client",
                        "name": "WLAN-FE",
                        "clienttype": "tcp",
                        "bufferCommands": true,
                        "stateLogEnabled": false,
                        "queueLogEnabled": false,
                        "tcpHost": "192.168.0.250",
                        "tcpPort": "502",
                        "tcpType": "TCP-RTU-BUFFERED",
                        "serialPort": "/dev/ttyUSB",
                        "serialType": "RTU-BUFFERD",
                        "serialBaudrate": "9600",
                        "serialDatabits": "8",
                        "serialStopbits": "1",
                        "serialParity": "none",
                        "serialConnectionDelay": "100",
                        "serialAsciiResponseStartDelimiter": "",
                        "unit_id": "1",
                        "commandDelay": "1",
                        "clientTimeout": "60000",
                        "reconnectOnTimeout": true,
                        "reconnectTimeout": "10000",
                        "parallelUnitIdsAllowed": true
                    }
                ]
                

                Kopieren und Importieren dann Wlan-FE anpassen
                02472f2a-95d4-4d83-8294-38e6ec7ffdab-image.png

                J 1 Reply Last reply Reply Quote 0
                • J
                  joeysch @joeysch last edited by

                  Noch vergessen, vorher natürlich die entsprechenden Datenpunkte einrichten.

                  1 Reply Last reply Reply Quote 0
                  • W
                    warp-it @badsnoopy667 last edited by

                    Hallo,
                    meine PV mit Huawei WR kommt (hoffentlich) nächste Woche, aber ich habe schon einmal Node Red auf IOBroker aufgesetzt und Deinen Flow (Vielen Dank) importiert. Wie kommt es, dass einige 'IOBroker Out Nodes' im Status 'connected' angezeigt werden, obwohl 0_userdata.0.Huawei nicht existiert?

                    2022-05-17 11_06_27-Node-RED _ iobroker.jpg

                    J 1 Reply Last reply Reply Quote 0
                    • J
                      joeysch @warp-it last edited by

                      @warp-it
                      Also der Flow ist nicht von mir, sondern hier aus dem Forum. Ich möchte mich nicht mit fremden Federn schmücken.

                      @warp-it said in [HowTo] Huawei SUN2000 WR Modbus mit node-red (read + write):

                      Wie kommt es, dass einige 'IOBroker Out Nodes' im Status 'connected' angezeigt werden, obwohl 0_userdata.0.Huawei nicht existiert?

                      Kann es sein, das die IP-Adresse die in der Wlan-Fe angegeben ist bei dir von einem Gerät belegt ist und er dahin connected?

                      W 1 Reply Last reply Reply Quote 0
                      • W
                        warp-it @joeysch last edited by

                        @joeysch said in [HowTo] Huawei SUN2000 WR Modbus mit node-red (read + write):

                        Kann es sein, das die IP-Adresse die in der Wlan-Fe angegeben ist bei dir von einem Gerät belegt ist und er dahin connected?

                        Nö, die in WLAN-FE eingetragene IP-Adresse existiert in meinem LAN nicht.

                        J 1 Reply Last reply Reply Quote 0
                        • M
                          micklafisch @badsnoopy667 last edited by

                          @badsnoopy667

                          Danke für die Top Anleitung, mit dem Modbus Adapter bin ich verzweifelt. Jetzt nach etwas Recherche bin ich auf deine Anleitung über NodeRed gestoßen und siehe da.... es geht auf anhieb.

                          Da ich vorher noch nie mit NodeRed was zu tun hatte bin ich entsprechend wackelig auf den Beinen damit. Was ich nicht umgesetzt bekomme sind die Alarme bzw. der Status des Wechselrichters.

                          Dort sind ja als Datentyp "Bitfield16" hinterlegt (z.b. Adresse 32000). So bekomme ich das aktuell in einen State geschrieben: [[{"bits":[0,1,1,0,0,0,0,0,0,0,0,0,0,0,0,0],"bit0":0,"bit1":1,"bit2":1,"bit3":0,"bit4":0,"bit5":0,"bit6":0,"bit7":0,"bit8":0,"bit9":0,"bit10":0,"bit11":0,"bit12":0,"bit13":0,"bit14":0,"bit15":0}]]

                          2158602e-df16-400f-b697-ce59e8d5f1bf-image.png

                          Jetzt wäre mein Ansatz es mit Blockly/JS zu zerlegen um an die Statis zu kommen. Aber gibt es ggf. mit NodeRed eine fluffigere Möglichkeit die einzelnen Bits direkt auszuwerten und nur wenn der Bitwert 1 ist auch ein State aktualisiert wird?

                          1 Reply Last reply Reply Quote 0
                          • S
                            Serial13579 last edited by Serial13579

                            Guten Tag zusammen,

                            ich konnte nun nach viel hin und her mich auf meinen Huawei WR einloggen als Installateur. Ich habe auf dem Dongle die Version 125 und beim WR 141. ich bekomme aber leider keine Verbindung hin die Einstellungen ehen für mich alle identisch aus. Welche IP Adresse muss denn eingetragen werden ? Die ich auf meinem Router für den Dongle sehe oder die IP Adresse die mir im Portal angezeigt wird ?
                            Ich weiß nicht mehr so recht weiter

                            PS. und wo finde ich den die MBus Einstellungen ? Ich finde die weder beim WR noch beim Dongle

                            PS bei mir war es die Version vom Dongle, für alle die noch Probleme haben, mit der Version 127 hat es geklappt.

                            Gruß

                            1 Reply Last reply Reply Quote 0
                            • S
                              Serial13579 last edited by

                              Moin,

                              leider habe ich immernoch 2 Probleme, das erste wäre das ich vom Meter den Datenpunkt: 0_userdata.0.Huawei.Meter.Active_Power nicht geschrieben bekomme, die anderen 4 wie Freqeuenz und Spannung sind da. Jemand eine Idee ?
                              Und es steht noch folgendes im Log für viele Datenpunkte: State value to set for "0_userdata.0.Huawei.Meter.Active_Power" has to be stringified but received type "number"

                              Muss ich den Typ für jeden Datenpunkt ändern ?

                              Gruß

                              B Z 2 Replies Last reply Reply Quote 0
                              • B
                                badsnoopy667 @Serial13579 last edited by

                                @serial13579 said in [HowTo] Huawei SUN2000 WR Modbus mit node-red (read + write):

                                das erste wäre das ich vom Meter den Datenpunkt: 0_userdata.0.Huawei.Meter.Active_Power nicht geschrieben bekomme

                                Du schreibst "geschrieben bekomme". Ich denke, Du meinst "lesen", oder? Schreiben kann man diesen Datenpunkt im WR nicht. Kommt denn irgend eine Art von Fehlermeldung? Hast Du mal versucht NUR diesen einen Datenpunkt zu lesen und alle anderen zu deaktivieren? Vielleicht stimmt was nicht mit der Abfragehäufigkeit.

                                1 Reply Last reply Reply Quote 0
                                • kep42010
                                  kep42010 last edited by kep42010

                                  Hallo zusammen,

                                  leider bekomme ich keine Verbindung zu meinem Wechselrichter aufgebaut. Hab versucht mich soweit es geht an die Anleitung zu halten (da Laie). Ggf. könnt ihr mir anhand der Screenshots ein paar Tipps geben:

                                  • WR ist ins Lan eingebunden. Kann aber die Lan- und Wlan-Adresse anpingen
                                  • Sind meine Einstellungen soweit korrekt? Ich habe in der App auf Modbus TCP umgestellt, Unit ID würde ich als 1 interpretieren oder ist das falsch?
                                  • Die NPM Zusatzmodule habe ich installiert. Sollten diese in Node RED auch ersichtlich sein?
                                  • Dongle hat folgende Software-Nummer: V100R001C00SPC119

                                  Anbei noch einige Bilder der Einstellungen. IP-Adressen für Lan und Wlan sowie Unit IDs von 0-3 habe ich bereits versucht.

                                  Besten Dank schon mal.

                                  node red.JPG node red flow.JPG modbus client.JPG IMG_7268.PNG IMG_7267.PNG

                                  B 1 Reply Last reply Reply Quote 0
                                  • B
                                    badsnoopy667 @kep42010 last edited by

                                    @kep42010 said in [HowTo] Huawei SUN2000 WR Modbus mit node-red (read + write):

                                    Dongle hat folgende Software-Nummer: V100R001C00SPC141

                                    @Serial13579 hat oben geschrieben, dass es bei Ihm mit Version 127 geklappt hat. Hast Du mal versucht auf diese Version zu gehen?

                                    kep42010 1 Reply Last reply Reply Quote 0
                                    • kep42010
                                      kep42010 last edited by

                                      @Serial13579 hat oben geschrieben, dass es bei Ihm mit Version 127 geklappt hat. Hast Du mal versucht auf diese Version zu gehen?

                                      @badsnoopy667 Nein noch nicht. Muss ich mal sehen wie ein Downgrade geht.

                                      1 Reply Last reply Reply Quote 0
                                      • A
                                        Aquin last edited by Aquin

                                        Guten Abend,

                                        auch ich habe verschiedene Weg ausprobiert um mein WR in IO-Broker zu intrigieren.
                                        Schließlich bin ich auch bei Node Red gelandet 😬.
                                        Nur leider bin ich hier absoluter Anfänger.

                                        Ich habe erfolgreich eine Verbindung herstellen können "danke an alle, die an dem Flow mitgearbeitet haben und ihre Tipps bereitgestellt haben".

                                        Damit ich besser meine Fehlersuche eingrenzen kann, habe ich diesen erst einmal verkleinert.
                                        Meine Wert werden auch aktualisiert und sind plausibel, nur leider bekomme ich ca. alle 2min folgende Fehlermeldung.

                                        e97b5598-b491-42fc-9f63-38c326ffd832-image.png.

                                        Nach einigem Suchen habe ich in den Einstellungen folgendes gefunden, hat dieses etwas damit zu tun oder muss ich wo anders suchen ? Oder kann ich die Fehlermeldung ignorieren?

                                        509fb134-f68e-4776-87dd-f58896656138-image.png

                                        Danke für eure Hilfe

                                        B 1 Reply Last reply Reply Quote 0
                                        • B
                                          badsnoopy667 @Aquin last edited by

                                          @aquin
                                          Diese Fehlermeldung bekomme ich auch sporadisch. Aktuell z.B. auch gerade wieder... aber bisher hat das noch keinen negativen Einfluss auf das Auslesen der Werte gehabt. Ich weiß nicht, was das Problem ist, aber bisher hat ignorieren gut funktioniert.

                                          1 Reply Last reply Reply Quote -1
                                          • kep42010
                                            kep42010 @badsnoopy667 last edited by kep42010

                                            @badsnoopy667 so ich bin nun einen guten Schritt weiter. Die von mir genannte SPC-Nummer hat scheinbar nicht gestimmt. Im Onlineportal wird der Dongle mit SPC119 angezeigt. Nun habe ich die SPC127 über den Support bekommen, habe hier aber noch Probleme mit dem Update....unter Wartung wird die neue Firmware nicht angezeigt. Weiß jemand in welchen Ordner man das File ablegen muss um es dann auswählen zu können?

                                            PS: Ich nutze ein iPhone, falls dies das Problem ist.

                                            Jedoch gehe ich davon aus, dass nach dem Update die Verbindung per node red klappt 🤙

                                            B 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate

                                            1.1k
                                            Online

                                            31.7k
                                            Users

                                            79.7k
                                            Topics

                                            1.3m
                                            Posts

                                            110
                                            573
                                            176271
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo