    • Homoran
      Homoran Global Moderator Administrators @SmartHomer 0 last edited by

      @smarthomer-0 sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

      innerhalb von 3 Monaten beide SDM72 kplt. ausgefallen (keine Modbus-Kommunikation, Display dunkel, spannungsfrei schalten bringt auch nichts).
      Ich denke, das Problem scheint bekannt zu sein, denn die Zähler werden anstandslos getauscht.

      genau. Eine Charge soll einen Bestückungsfehler gehabt haben. (kalte Lötstelle??)

      Ich hatte auch diese Symptome (innerhalb 2 Monaten) und beim 2. war dann der Fehler bekannt und alle 5 wurden getauscht.

      Das ist jetzt Monate her und es gab kein weiteres Problem.
      Auch mein gleichzeitig gekaufter SDM 630 hat keine Probleme.

      K 1 Reply Last reply Reply Quote 2
      • K
        klassisch Most Active @omega235 last edited by

        @omega235 sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

        @klassisch

        Dieser Converter von Amazon funktioniert auch und ist deutlich billiger (und von der größe mMn besser):

        Vielen Dank für den Hinweis. Hast Du das Gerät selbst im EInsatz? Falls Ja, kann ich das im Eingangspost erwähnen.
        Welche Spannung benötigt das Gerät.
        Ich hatte für die WiFi-Bastelmodule ca. 8 EUR bezahlt. AP Kunststoff-Dose dazu und fertig.

        omega235 1 Reply Last reply Reply Quote 0
        • K
          klassisch Most Active @SmartHomer 0 last edited by

          @smarthomer-0 sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

          Insofern habe ich jetzt einen neuen Energiezähler-Typ verbaut: Finder 7M.38.8.400.02.12 MID.
          Funktioniert ebenfalls mit ModBus-Schnittstelle am ioBroker Doku ModBus-Schnittstelle Finder 7M.38.

          Vielen Dank für den Hinweis. Kostet etwa 90 bis 100 EUR?
          Finder ist ein rennomierte Marke im Bereich der Elektroinstallation. Ich habe auch Finder Zeitrelais im Einsatz.

          S 1 Reply Last reply Reply Quote 0
          • K
            klassisch Most Active @Homoran last edited by

            @homoran sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

            genau. Eine Charge soll einen Bestückungsfehler gehabt haben. (kalte Lötstelle??)

            Ich hatte auch diese Symptome (innerhalb 2 Monaten) und beim 2. war dann der Fehler bekannt und alle 5 wurden getauscht.

            Das ist jetzt Monate her und es gab kein weiteres Problem.
            Auch mein gleichzeitig gekaufter SDM 630 hat keine Probleme.

            Vielen Dank für den Erfahrungsbericht. Mein SDM120 für die Heizung schnurrt noch immer.

            bahnuhr 1 Reply Last reply Reply Quote 0
            • Homoran
              Homoran Global Moderator Administrators @SmartHomer 0 last edited by

              @smarthomer-0 sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

              Weiterer Vorteil ist mE, dass bei der Erst-Inbetriebnahme einmalig eingestellt werden kann, wie der Zähler mit der Verrechnung von Bezug/Einspeisung umgeht

              das geht bei vielen anderen auch. Dort geht es aber um die Berechnung eines Wertes, der sich je nach Betrachtung des Bezuges und der Einspeisung ergibt. Also die Bilanz

              Das Problem ist, dass es nur selten eine "korrekte" Berechnung der Summe der Energien aus den drei Phasen für Bezug und Einspeisung gibt.

              1 Reply Last reply Reply Quote 1
              • S
                SmartHomer 0 @klassisch last edited by SmartHomer 0

                @klassisch sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

                Vielen Dank für den Hinweis. Kostet etwa 90 bis 100 EUR?

                Ja. der lag bei ca. € 85.
                Und Finder ist mir beruflich aus der Automatisierungstechnik eben auch mit guter Qualität bekannt.

                Homoran 1 Reply Last reply Reply Quote 0
                • Homoran
                  Homoran Global Moderator Administrators @SmartHomer 0 last edited by

                  @smarthomer-0 sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

                  . der lag bei ca. € 85.

                  WENN der dann die richtig saldierten Energiewerte liefern würde, ist er ja in der Preisklasse des SDM630.
                  das macht mich jetzt noch misstrauischer

                  S 1 Reply Last reply Reply Quote 0
                  • S
                    SmartHomer 0 @Homoran last edited by

                    @homoran
                    Wie gesagt - für meine Anwendung nicht rele

                    @homoran sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

                    @smarthomer-0 sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

                    Weiterer Vorteil ist mE, dass bei der Erst-Inbetriebnahme einmalig eingestellt werden kann, wie der Zähler mit der Verrechnung von Bezug/Einspeisung umgeht

                    das geht bei vielen anderen auch. Dort geht es aber um die Berechnung eines Wertes, der sich je nach Betrachtung des Bezuges und der Einspeisung ergibt. Also die Bilanz

                    Das Problem ist, dass es nur selten eine "korrekte" Berechnung der Summe der Energien aus den drei Phasen für Bezug und Einspeisung gibt.

                    Wie geschrieben: Für mich in meiner Anwendung nicht relevant und ich kann es leider auch nicht testen.

                    Im PV-Forum habe ich einen Eintrag in dieser Richtung gefunden: PV-Forum

                    Homoran 1 Reply Last reply Reply Quote 0
                    • Homoran
                      Homoran Global Moderator Administrators @SmartHomer 0 last edited by

                      @smarthomer-0 sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

                      Im PV-Forum habe ich einen Eintrag in dieser Richtung gefunden: PV-Forum

                      Danke!
                      Ist aber auch da ziemlich schwammig.
                      Bei den Leistungswerten (W) passt es ja auch bei SDM630&Co.

                      Die Energiewerte (kWh) sind leider das Problem.
                      in einem Nebensatz steht was von "genauso heraufzählen".

                      @smarthomer-0 sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

                      Für mich in meiner Anwendung nicht relevant

                      schade für uns. Eine klare Aussage für Zählerstände analog 1.8.0 und 2.8.0 wäre schon hilfreich.
                      Da mein SDM630 direkt hinter dem EVU Zähler hängt, müsste der Eli zum Austausch das gesamte Haus Stromlos machen. Nur zum Testen nicht wirklich realistisch.

                      Danke für die Infos!

                      1 Reply Last reply Reply Quote 0
                      • omega235
                        omega235 Developer @klassisch last edited by

                        @klassisch

                        Ja habe ihn seit heut im Einsatz. Konfig im Anhang.

                        der RJ45 ist kein LAN Port, sondern wird nur für Spannung und RS485 verwendet (gut markiert, kann man also auch direkt ein LAN-Kabel verwenden und die PINS entsprechend verkabeln).

                        Kommunikation läuft daher nur über WLAN!

                        Spannung ist 5-35V DC

                        Davor den Waveshare Hutschienen Converter gehabt, der hat auch funktioniert, ist aber zu groß um in einem normalen Sicherungskasten reinzupassen (höhe passt nicht da die Höhe zu breit (keine Ahnung wie ich es richtig beschreiben soll)

                        aca3eff3-8319-4683-857f-544ced34f76b-grafik.png
                        83df34d1-07f0-404c-9b19-0c2e50ab7314-grafik.png

                        K 1 Reply Last reply Reply Quote 1
                        • K
                          klassisch Most Active @omega235 last edited by

                          @omega235 ; @SmartHomer-0 ; @Homoran : Vielen Dank, hab die Infos im Eingangspost nachgetragen.

                          1 Reply Last reply Reply Quote 0
                          • bahnuhr
                            bahnuhr Forum Testing Most Active @klassisch last edited by

                            @klassisch

                            Ich muss jetzt auch mal nachfragen.
                            Habe im Betrieb: SDM72 mit waveshare rs485to eth
                            verbunden mit modbus Adapter
                            Läuft einwandfrei

                            Jetzt habe ich mir nochmal einen SDM72 und waveshare rs485towifi geleistet.
                            Alles verbunden; testweise nur mit einer Phase.
                            Und neue Instanz vom Adapter.
                            Aber irgendwie klappt die Verbindung nicht richtig (bzw. jetzt gar nicht mehr)

                            Anbei Screenshot vom Adapter:
                            99f5c66d-0350-46df-9811-8e6fa30788e5-image.png
                            615a7b1c-4c3f-40db-81d4-f6d7c6855bb3-image.png

                            Und nun vom waveshare rs485wifi
                            dea7eecf-01e6-41eb-a014-9e39876d542f-image.png
                            7a499546-29f6-4550-8bb0-7b66fb9339af-image.png
                            e243f624-a9ab-401f-89e9-e35e25c82100-image.png
                            c33da274-bb6b-493d-bf41-08aac36a8085-image.png
                            6f570ebb-c560-4027-8ffc-21bf22072607-image.png

                            Vielleicht findet jemand den Fehler.
                            Im log kommt nur:

                            modbus.1
                            2024-05-31 20:11:19.868	debug	Closing client on purpose.
                            modbus.1
                            2024-05-31 20:11:18.869	debug	Cleaning up request fifo.
                            modbus.1
                            2024-05-31 20:11:18.869	debug	Socket closed with error
                            modbus.1
                            2024-05-31 20:11:18.868	warn	On error: {"errno":-111,"code":"ECONNREFUSED","syscall":"connect","address":"192.168.243.144","port":503}
                            modbus.1
                            2024-05-31 20:11:18.868	error	Client in error state.
                            modbus.1
                            2024-05-31 20:11:18.868	error	Socket Error
                            

                            es kamen auch schon andere Meldungen, sowas:

                            modbus.1
                            2024-05-31 19:46:21.395	warn	Error in handler for 4: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 11. Received 12
                            modbus.1
                            2024-05-31 19:46:16.266	warn	Poll error count: 4 code: {"errorCode":148,"exceptionCode":127}
                            modbus.1
                            2024-05-31 19:46:16.245	warn	Error in handler for 4: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 11. Received 12
                            modbus.1
                            2024-05-31 19:46:11.115	warn	Poll error count: 3 code: {"errorCode":227,"exceptionCode":175}
                            modbus.1
                            2024-05-31 19:46:11.095	warn	Error in handler for 4: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 11. Received 12
                            modbus.1
                            2024-05-31 19:46:05.964	warn	Poll error count: 2 code: {"errorCode":141,"exceptionCode":123}
                            modbus.1
                            2024-05-31 19:46:05.945	warn	Error in handler for 4: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 11. Received 12
                            modbus.1
                            2024-05-31 19:46:00.814	warn	Poll error count: 1 code: "ReadInputRegisters: Invalid FC 1"
                            modbus.1
                            2024-05-31 19:46:00.786	warn	Error in handler for 4: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 11. Received 12
                            modbus.1
                            2024-05-31 19:45:55.182	warn	Poll error count: 10 code: {"err":"timeout","timeout":5000}
                            

                            Habt ihr ne einfache Anleitung wie man dieses waveshare wifi korrekt einrichtet.
                            Danke für Rückmeldungen.

                            mfg
                            Dieter

                            K 1 Reply Last reply Reply Quote 0
                            • K
                              klassisch Most Active @bahnuhr last edited by klassisch

                              @bahnuhr

                              • Warum Slave Id = 2? Ist das so im Gerät eingegeben?
                              • Warum ist der Waveshare als Client konfiguriert. Sollte der nicht Server sein? Wie beim LAN Waveshare auch?
                              • dort https://forum.iobroker.net/topic/1259/modbus-adapter/695?_=1717180010632 hat @Ronniboy eine Anleitung hinterlassen. Wobei er Vircom einsetzt, was meiner Meinung nach nicht erforderlich sein sollte
                              • Hier noch ein Hinweis von @SidM https://forum.iobroker.net/post/870092
                              bahnuhr 2 Replies Last reply Reply Quote 1
                              • bahnuhr
                                bahnuhr Forum Testing Most Active @klassisch last edited by

                                @klassisch
                                Danke, schau ich mir an.

                                1 Reply Last reply Reply Quote 0
                                • bahnuhr
                                  bahnuhr Forum Testing Most Active @klassisch last edited by

                                  @klassisch
                                  Ja, id hab ich beim SDM72 eingegeben
                                  (hatte erst vor dies in Reihe zu schalten um 1 Instanz nur zu benötigen)
                                  Nun sitzt der SDM aber woanders.

                                  Die Hinweise hab ich mir angeschaut.
                                  Dachte eigentlich, dass dies so passt.

                                  Bekomme trotzdem:

                                  modbus.1
                                  2024-05-31 20:46:44.021	warn	Poll error count: 3 code: {"err":"timeout","timeout":5000}
                                  modbus.1
                                  2024-05-31 20:46:44.020	error	Client in error state.
                                  modbus.1
                                  2024-05-31 20:46:44.020	error	Request timed out.
                                  modbus.1
                                  2024-05-31 20:46:44.019	warn	Error: undefined
                                  modbus.1
                                  2024-05-31 20:46:39.018	debug	[DevID_2/inputRegs] Poll address 0 - 8 registers
                                  modbus.1
                                  2024-05-31 20:46:39.018	debug	[DevID_2] Poll start ---------------------
                                  modbus.1
                                  2024-05-31 20:46:39.017	info	Connected to slave 192.168.243.144
                                  

                                  Und die Instanz bleibt unten rot:
                                  10dff142-99ea-4fdf-9bb3-a2b040820b76-image.png

                                  K 1 Reply Last reply Reply Quote 0
                                  • K
                                    klassisch Most Active @bahnuhr last edited by

                                    @bahnuhr Schau Dir mal die Konfig von @SidM an https://forum.iobroker.net/assets/uploads/files/1665226770066-664ac22c-a54b-43b8-a74d-860f53a3f909.jpeg

                                    Der Waveshare ist der Server und der Modbus Adapter im ioBroker ist der Client, der beim Server die Daten abholt bzw. abonniert

                                    bahnuhr 1 Reply Last reply Reply Quote 0
                                    • bahnuhr
                                      bahnuhr Forum Testing Most Active @klassisch last edited by

                                      @klassisch
                                      Ja, müsste ich aber doch haben:
                                      Einstellung waveshare:
                                      94a38ae5-9c81-49c1-977f-07c69c95f2c7-image.png

                                      und iob:
                                      834abe10-a864-4669-88e4-7a811ec55e7a-image.png

                                      Und im log kommt:

                                      modbus.1
                                      2024-05-31 21:06:27.018	warn	Poll error count: 5 code: {"errorCode":203,"exceptionCode":75}
                                      modbus.1
                                      2024-05-31 21:06:27.018	debug	Received pdu describes an error.
                                      modbus.1
                                      2024-05-31 21:06:26.998	warn	Error in handler for 4: RangeError [ERR_OUT_OF_RANGE]: The value of "offset" is out of range. It must be >= 0 and <= 11. Received 12
                                      modbus.1
                                      2024-05-31 21:06:26.890	debug	[DevID_2/inputRegs] Poll address 0 - 14 registers
                                      modbus.1
                                      2024-05-31 21:06:26.890	debug	[DevID_2] Poll start ---------------------
                                      

                                      Ich raffs nicht.
                                      Mit dem andere waveshare hat es auf Anhieb geklappt.
                                      Nur dieser muckt rum.

                                      K 1 Reply Last reply Reply Quote 0
                                      • K
                                        klassisch Most Active @bahnuhr last edited by

                                        @bahnuhr
                                        Was Du noch testen kannst: Die Modbus RTU Wandlung in den ioBroker Adapter verlegen und dann beim Waveshare nur TCP wählen

                                        bahnuhr 2 Replies Last reply Reply Quote 0
                                        • bahnuhr
                                          bahnuhr Forum Testing Most Active @klassisch last edited by

                                          @klassisch sagte in SDM120 SDM72 SDM630 Modbus RS485 Stromzähler (W)LAN ioBroker:

                                          @bahnuhr
                                          Was Du noch testen kannst: Die Modbus RTU Wandlung in den ioBroker Adapter verlegen und dann beim Waveshare nur TCP wählen

                                          Klappt alles nicht.

                                          Ich gebs auf mit dem Wifi Teil.

                                          Habe noch einen Waveshare RS485toRJ45 rum liegen.
                                          Mit diesem hat es gleich geklappt.

                                          Alles komisch das ganze.

                                          1 Reply Last reply Reply Quote 1
                                          • bahnuhr
                                            bahnuhr Forum Testing Most Active @klassisch last edited by

                                            @klassisch
                                            Danke für die positive Bewertung.
                                            Ich hätte es aber lieber hinbekommen.

                                            K 1 Reply Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate

                                            834
                                            Online

                                            31.7k
                                            Users

                                            79.7k
                                            Topics

                                            1.3m
                                            Posts

                                            modbus modbus rtu rs485 sdm120 sdm630 sdm72 stromzähler tcprs485 wandler