    JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.

    This topic has been deleted. Only users with topic management privileges can see it.
    • Elektroniker86
      Elektroniker86 last edited by

      Hat jemand eine Idee wie ich die Adressen hier eintragen muss?

      Screenshot 2025-03-05 233835.png Screenshot 2025-03-05 233607.png

      Homoran 1 Reply Last reply Reply Quote 0
      • Homoran
        Homoran Global Moderator Administrators @Elektroniker86 last edited by

        @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

        @homoran
        Stecker besorgen und Bus abgreifen ist keine Option?

        Doch!
        Das war ja der Hintergrund meiner Frage

        @homoran sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

        Wie kommst du an den Bus?
        Was für ein Kabel, welche Buchse?

        Kabel enthält Stecker 😉

        lobomau 1 Reply Last reply Reply Quote 0
        • Homoran
          Homoran Global Moderator Administrators @Elektroniker86 last edited by

          @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

          Hat jemand eine Idee wie ich die Adressen hier eintragen muss?

          Wir können es mal versuchen

          Adresse von Hex in Dezimal umrechnen,
          Du hast mehrere Slaves angewählt, dann muss die Slave-ID deines BMS in die nächste Spalte

          Name, Beschreibung Einheit ist selbsterklärend

          Format steht ja auch in der Tabelle (U)Int16/32

          Dann sollte es "nur noch" auf die Grundeinstellungen ankommen

          1 Reply Last reply Reply Quote 0
          • wendy2702
            wendy2702 last edited by

            @elektroniker86 Laut dem verlinkten Thread Geschwindigleit auf 115200, 8 Daten Bits, 1 Stop Bit

            Function Code 03H wären zum Lesen Holding Register

            cddf4d4a-25cd-4195-a6a3-4f482e318593-grafik.png

            7ef527d7-7ee4-4ca0-a4fa-0b80bf5d832b-grafik.png

            Aus dem Document würde ich zum testen mal damit beginnen:

            821a8deb-373c-47b4-a8ba-e4e4828048eb-grafik.png

            1200H + 0090H = 1290H = 4752Dez für z.B. Total Battery Voltage BatVol in "mV"

            Unint32 litte oder big endian usw. muss man mal aus testen.

            Elektroniker86 1 Reply Last reply Reply Quote 2
            • Elektroniker86
              Elektroniker86 @wendy2702 last edited by Elektroniker86

              @wendy2702

              Vielen Dank erstmal für deine Hilfe!
              Ich habe mal getestet, jedoch leider ohne Erfolg.
              Big und little endian habe ich schon probiert.....

              Screenshot 2025-03-06 124948.png

              Screenshot 2025-03-06 124926.png

              Screenshot 2025-03-06 124848.png

              Das sind die einstellungen, Adapter wird und bleibt grün und folgendes steht im Log:

              
              
              modbus.5
              2025-03-06 12:58:48.249	info	Connected to slave 192.168.1.123
              
              modbus.5
              2025-03-06 12:58:48.206	info	Can not execute task add for ID undefined: Parameter "id" needs to be of type "string" but type "undefined" has been passed
              
              modbus.5
              2025-03-06 12:58:48.160	error	Invalid object: {"type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"mV"},"native":{"regType":"inputRegs","address":-25249,"deviceId":0,"type":"uint32le","len":2,"offset":"0","factor":"1"}}
              
              modbus.5
              2025-03-06 12:58:48.160	error	Invalid data inputRegisters/0: {"_address":"4752","deviceId":0,"name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32le","len":2,"factor":"1","offset":"0","formula":"","role":"value","room":"","cw":false,"isScale":false,"address":-25249,"fullId":"modbus.5.0"}
              
              modbus.5
              2025-03-06 12:58:48.160	error	Invalid inputRegisters address: -25249
              
              modbus.5
              2025-03-06 12:58:48.098	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
              
              1 Reply Last reply Reply Quote 0
              • Elektroniker86
                Elektroniker86 last edited by

                Ich muss noch dazu sagen, dass es 2 Batterien sind mit den identischen JKBMS und gleiche Firmware.
                Damit das mit dem Wechselrichter richtig funktioniert muss eine Batterie mit den DIP Switches auf Adresse 0 (Master) eingestellt werden und die 2. wird dann auf die Adresse 1 eingestellt.......

                Mit der PC Software kann ich mich verbinden, mit z.B Adresse 1, dann kann ich oben bei den Reitern Device 0 und Device 1 wählen und die Werte abrufen.

                Screenshot 2025-03-06 130917.png

                wendy2702 1 Reply Last reply Reply Quote 0
                • wendy2702
                  wendy2702 @Elektroniker86 last edited by

                  @elektroniker86 zwei Sachen fallen mir am Handy auf.

                  Haken bei Aliases verwenden raus, danach Register kontrollieren.

                  Testen

                  Wenn kein unterschied: Haken bei mehrere IDs verwenden raus und Slave ID vorne einstellen in der Instanz und nicht in den Registern.

                  Was ich am Dokument noch merkwürdig finde ist die Angabe von Uint32 mit Länge 4, eigentlich ist Unit 32 Länge 2.

                  Man könnte dann auch mal mit uint64 versuchen.
                  Alternativ mit externem Modbus Programm und erst wann da was kommt weiter mit iob

                  Elektroniker86 1 Reply Last reply Reply Quote 0
                  • Elektroniker86
                    Elektroniker86 @wendy2702 last edited by

                    @wendy2702

                    So habe noch etwas rumprobiert, so wie du gesagt hast, unit 64 usw.
                    Jetzt bleibt der Adapter nicht grün und folgendes im Log.

                    
                    
                    modbus.5
                    2025-03-06 13:38:51.574	error	Client in error state.
                    
                    modbus.5
                    2025-03-06 13:38:51.574	error	Request timed out.
                    
                    modbus.5
                    2025-03-06 13:38:51.573	warn	Error: undefined
                    
                    modbus.5
                    2025-03-06 13:38:45.521	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
                    
                    modbus.5
                    2025-03-06 13:38:45.521	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                    
                    modbus.5
                    2025-03-06 13:38:45.521	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                    
                    modbus.5
                    2025-03-06 13:38:41.500	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                    
                    modbus.5
                    2025-03-06 13:38:36.469	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                    
                    modbus.5
                    2025-03-06 13:37:50.820	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                    
                    modbus.5
                    2025-03-06 13:37:50.820	error	Client in error state.
                    
                    modbus.5
                    2025-03-06 13:37:50.820	error	Request timed out.
                    
                    modbus.5
                    2025-03-06 13:37:50.819	warn	Error: undefined
                    
                    modbus.5
                    2025-03-06 13:37:44.768	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
                    
                    modbus.5
                    2025-03-06 13:37:41.418	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                    
                    modbus.5
                    2025-03-06 13:37:36.407	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                    
                    modbus.5
                    2025-03-06 13:36:56.950	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                    
                    modbus.5
                    2025-03-06 13:36:56.950	error	Client in error state.
                    
                    modbus.5
                    2025-03-06 13:36:56.949	error	Request timed out.
                    
                    modbus.5
                    2025-03-06 13:36:56.949	warn	Error: undefined
                    
                    modbus.5
                    2025-03-06 13:36:50.897	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
                    
                    modbus.5
                    2025-03-06 13:36:46.898	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                    
                    modbus.5
                    2025-03-06 13:36:41.846	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                    
                    

                    Welches PC Programm kannst du zum testen empfehlen?

                    wendy2702 1 Reply Last reply Reply Quote 0
                    • wendy2702
                      wendy2702 @Elektroniker86 last edited by

                      @elektroniker86 kann man, wenn die Instanz im Expertenmodus ist, bei Uint32 die Länge auf 4 Stellen?

                      Komme gerade nicht an meine Installation zum probieren.

                      Elektroniker86 1 Reply Last reply Reply Quote 0
                      • Elektroniker86
                        Elektroniker86 @wendy2702 last edited by

                        @wendy2702

                        Nein, kann man nicht umstellen weder normal noch im Expertenmodus.....
                        Wie du sagtest u32 ist 2 nicht 4 die Spalte wird dann ausgegraut.

                        wendy2702 1 Reply Last reply Reply Quote 0
                        • lobomau
                          lobomau @Homoran last edited by

                          @homoran du hast doch auch victron, oder?
                          Ich mache den Umweg über den victron-controller (raspi 4). Meine beiden JK BMS sind am raspi angeschlossen. Über modbus hole ich mir die JK BMS Daten vom Victron:

                          ea7bed27-cf28-4815-a0ab-4f441a18eca1-{8E75C88F-33B9-4B67-8314-F8039AD791EE}.png

                          c73cbd47-7f59-4974-a5bf-c6c9ccb082f3-{0B309EBF-F119-4550-AC17-1205E31B806C}.png

                          Homoran 1 Reply Last reply Reply Quote 1
                          • Homoran
                            Homoran Global Moderator Administrators @lobomau last edited by Homoran

                            @lobomau sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                            du hast doch auch victron, oder?

                            ja, und oder 😉

                            hier geht's ums Wohnmobil.
                            Hab da eine LiFeYPO4 "12V" Batterie mit JK-BMS

                            Der Raspi mit Venus OS und Display ist fertig.
                            Genau dafür such ich was

                            1 Reply Last reply Reply Quote 0
                            • wendy2702
                              wendy2702 @Elektroniker86 last edited by

                              @elektroniker86 kannst du mal das log zeigen wenn du den haken bei Aliase draußen hast, die Device ID vorne eingetragen ist. Dann auch noch mal die Einstellungen Instanz und Konverter

                              1 Reply Last reply Reply Quote 0
                              • Elektroniker86
                                Elektroniker86 last edited by

                                Ich komme nicht weiter, hier die logs:

                                
                                modbus.5
                                2025-03-06 16:23:30.302	info	Disconnected from slave 192.168.1.123
                                
                                modbus.5
                                2025-03-06 16:23:29.302	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                                
                                modbus.5
                                2025-03-06 16:23:29.302	error	Client in error state.
                                
                                modbus.5
                                2025-03-06 16:23:29.302	error	Request timed out.
                                
                                modbus.5
                                2025-03-06 16:23:29.301	warn	Error: undefined
                                
                                modbus.5
                                2025-03-06 16:23:23.250	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
                                
                                modbus.5
                                2025-03-06 16:23:23.249	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                                
                                modbus.5
                                2025-03-06 16:23:23.249	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                                
                                wendy2702 Homoran 2 Replies Last reply Reply Quote 0
                                • wendy2702
                                  wendy2702 @Elektroniker86 last edited by

                                  @elektroniker86 Da müssen wir auch die Einstellungen zu sehen.

                                  Elektroniker86 1 Reply Last reply Reply Quote 0
                                  • Homoran
                                    Homoran Global Moderator Administrators @Elektroniker86 last edited by

                                    @elektroniker86 stell mal bitte auf debug

                                    Ansonsten

                                    @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                    "ReadInputRegisters: Invalid FC 32"

                                    @wendy2702 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                    Function Code 03H wären zum Lesen Holding Register

                                    1 Reply Last reply Reply Quote 0
                                    • Elektroniker86
                                      Elektroniker86 @wendy2702 last edited by

                                      @wendy2702

                                      Moment da hat sich was überschnitten Das ist jetzt aktuell.

                                      Screenshot 2025-03-06 170913.png Screenshot 2025-03-06 170846.png Screenshot 2025-03-06 170813.png

                                      
                                      modbus.5
                                      2025-03-06 17:10:00.444	info	Disconnected from slave 192.168.1.123
                                      
                                      modbus.5
                                      2025-03-06 17:09:59.443	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                                      
                                      modbus.5
                                      2025-03-06 17:09:59.443	error	Client in error state.
                                      
                                      modbus.5
                                      2025-03-06 17:09:59.443	error	Request timed out.
                                      
                                      modbus.5
                                      2025-03-06 17:09:59.442	warn	Error: undefined
                                      
                                      modbus.5
                                      2025-03-06 17:09:53.391	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
                                      
                                      modbus.5
                                      2025-03-06 17:09:53.390	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                                      
                                      modbus.5
                                      2025-03-06 17:09:53.390	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                                      
                                      modbus.5
                                      2025-03-06 17:09:48.990	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                                      
                                      modbus.5
                                      2025-03-06 17:09:43.902	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                                      
                                      modbus.5
                                      2025-03-06 17:09:43.788	info	Connected to slave 192.168.1.123
                                      
                                      modbus.5
                                      2025-03-06 17:09:43.634	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                                      
                                      modbus.5
                                      2025-03-06 17:09:39.643	info	terminating
                                      
                                      modbus.5
                                      2025-03-06 17:09:39.159	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                      
                                      modbus.5
                                      2025-03-06 17:09:39.158	info	terminating
                                      
                                      modbus.5
                                      2025-03-06 17:09:39.142	info	Got terminate signal TERMINATE_YOURSELF
                                      
                                      
                                      Homoran 1 Reply Last reply Reply Quote 0
                                      • Homoran
                                        Homoran Global Moderator Administrators @Elektroniker86 last edited by

                                        @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                        Das ist jetzt aktuell.

                                        bitte erst einmal nur ein Register abrufen.
                                        Input <-> Holding gilt immer noch

                                        Elektroniker86 1 Reply Last reply Reply Quote 0
                                        • Elektroniker86
                                          Elektroniker86 @Homoran last edited by

                                          @homoran

                                          So, ein Register und Debug:

                                          
                                          modbus.5
                                          2025-03-06 17:14:13.892	info	Disconnected from slave 192.168.1.123
                                          
                                          modbus.5
                                          2025-03-06 17:14:13.892	debug	Closing client on purpose.
                                          
                                          modbus.5
                                          2025-03-06 17:14:12.892	debug	Cleaning up request fifo.
                                          
                                          modbus.5
                                          2025-03-06 17:14:12.892	debug	Clearing timeout of the current request.
                                          
                                          modbus.5
                                          2025-03-06 17:14:12.892	debug	Socket closed with error
                                          
                                          modbus.5
                                          2025-03-06 17:14:12.891	warn	[DevID_1] Poll error count: 3 code: {"err":"timeout","timeout":5000}
                                          
                                          modbus.5
                                          2025-03-06 17:14:12.891	error	Client in error state.
                                          
                                          modbus.5
                                          2025-03-06 17:14:12.891	error	Request timed out.
                                          
                                          modbus.5
                                          2025-03-06 17:14:12.891	warn	Error: undefined
                                          
                                          modbus.5
                                          2025-03-06 17:14:07.890	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
                                          
                                          modbus.5
                                          2025-03-06 17:14:07.889	debug	[DevID_1] Poll start ---------------------
                                          
                                          modbus.5
                                          2025-03-06 17:14:06.839	warn	[DevID_1] Poll error count: 2 code: "ReadInputRegisters: Invalid FC 32"
                                          
                                          modbus.5
                                          2025-03-06 17:14:04.028	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
                                          
                                          modbus.5
                                          2025-03-06 17:14:04.028	debug	[DevID_1] Poll start ---------------------
                                          
                                          modbus.5
                                          2025-03-06 17:14:02.975	warn	[DevID_1] Poll error count: 1 code: "App Timeout"
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.793	warn	Error in handler for 4: RangeError [ERR_BUFFER_OUT_OF_BOUNDS]: Attempt to access memory outside buffer bounds
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.776	debug	[DevID_1/inputRegs] Poll address 4752 - 2 registers
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.776	debug	Initialization of scale factors done!
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.775	debug	[DevID_1] Poll start ---------------------
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.775	info	Connected to slave 192.168.1.123
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.721	debug	Remove old object modbus.5.inputRegisters.4774_soc
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.677	debug	Initialize Objects for holdingRegs: []
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.677	debug	Add inputRegisters.4752_Total_Battery_Voltage: {"_id":"inputRegisters.4752_Total_Battery_Voltage","type":"state","common":{"name":"bat vol","role":"value","type":"number","read":true,"write":false,"def":0,"unit":"mV"},"native":{"regType":"inputRegs","address":4752,"deviceId":1,"type":"uint32be","len":2,"offset":0,"factor":1}}
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.677	debug	Initialize Objects for inputRegs: [{"_address":4752,"deviceId":1,"name":"Total Battery Voltage","description":"bat vol","unit":"mV","type":"uint32be","len":2,"factor":1,"offset":0,"formula":"","role":"value","room":"","cw":false,"isScale":false,"address":4752,"id":"inputRegisters.4752_Total_Battery_Voltage"}]
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.676	debug	Initialize Objects for coils: []
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.676	debug	Initialize Objects for disInputs: []
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.621	info	starting. Version 6.3.2 in /opt/iobroker/node_modules/iobroker.modbus, node: v20.18.3, js-controller: 7.0.6
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.502	debug	Plugin sentry Initialize Plugin (enabled=true)
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.487	debug	States connected to redis: 0.0.0.0:9000
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.433	debug	States create User PubSub Client
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.433	debug	States create System PubSub Client
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.424	debug	Redis States: Use Redis connection: 0.0.0.0:9000
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.406	debug	Objects connected to redis: 0.0.0.0:9001
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.405	debug	Objects client initialize lua scripts
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.376	debug	Objects create User PubSub Client
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.376	debug	Objects create System PubSub Client
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.375	debug	Objects client ready ... initialize now
                                          
                                          modbus.5
                                          2025-03-06 17:13:57.358	debug	Redis Objects: Use Redis connection: 0.0.0.0:9001
                                          
                                          modbus.5
                                          2025-03-06 17:13:53.655	info	terminating
                                          
                                          modbus.5
                                          2025-03-06 17:13:53.169	info	Terminated (ADAPTER_REQUESTED_TERMINATION): Without reason
                                          
                                          modbus.5
                                          2025-03-06 17:13:53.169	debug	Plugin sentry destroyed
                                          
                                          modbus.5
                                          2025-03-06 17:13:53.169	info	terminating
                                          
                                          modbus.5
                                          2025-03-06 17:13:53.154	debug	Closing client on purpose.
                                          
                                          modbus.5
                                          2025-03-06 17:13:53.154	info	Got terminate signal TERMINATE_YOURSELF
                                          
                                          Homoran 1 Reply Last reply Reply Quote 0
                                          • Homoran
                                            Homoran Global Moderator Administrators @Elektroniker86 last edited by

                                            @elektroniker86 sagte in JK BMS mit Modbus Adapter über RS485 zu TCP einbinden.:

                                            Add inputRegisters

                                            bitte Holdingregister nehmen

                                            wendy2702 Elektroniker86 2 Replies Last reply Reply Quote 0
                                            • First post
                                              Last post

                                            Support us

                                            ioBroker
                                            Community Adapters
                                            Donate

                                            971
                                            Online

                                            31.7k
                                            Users

                                            79.7k
                                            Topics

                                            1.3m
                                            Posts

                                            5
                                            92
                                            3054
                                            Loading More Posts
                                            • Oldest to Newest
                                            • Newest to Oldest
                                            • Most Votes
                                            Reply
                                            • Reply as topic
                                            Log in to reply
                                            Community
                                            Impressum | Datenschutz-Bestimmungen | Nutzungsbedingungen
                                            The ioBroker Community 2014-2023
                                            logo